Discuss EICR Repairs. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
65
Hi
If you go behind another electrician who has failed an EICR on something minor, like a couple of broken pendants or something, you carry out the repairs and issue a minor works, the client would then have an unsatisfactory EICR and a minor works cert stating that the C2 items have been rectified.
The original EICR has a 1 month till next inspection date so would these 2 documents together give a OK for 5 years outcome?
 
Hi
If you go behind another electrician who has failed an EICR on something minor, like a couple of broken pendants or something, you carry out the repairs and issue a minor works, the client would then have an unsatisfactory EICR and a minor works cert stating that the C2 items have been rectified.
The original EICR has a 1 month till next inspection date so would these 2 documents together give a OK for 5 years outcome?
The short answer is yes - the law does not require a 'satisfactory' report to be generated - just that any necessary remedial works (generally C2s) after an inspection is completed within 28 days and that this can be proved where necessary.

It may be sensible to note in the MWC the work specifically in a way that cross references with the certificate - maybe even quote the certificate number?

In practice if letting agents are involved, they tend not to see much past the front page though, so sometimes seem to be demanding a bit of paper with 'satisfactory' on.
 
Just been asked to do the repairs on a couple of fails and test some other properties they have got.
If its just a broken socket or something minor like that once i have completed the test I normally just change them if its the difference between a pass and a fail and so far the clients don't seem to mind, I always take pictures of before and after still.
They have been quoted £90 to change 2 pendants that the blue and brown are showing outside the cap where its stretched over the years, seems quite a bit to me but not sure as they will also get a Satisfactory EICR, I can only issue a minor works to go with the unsatisfactory one but i know with letting agents they only look at page 1.
 
Yes I agree.
Think they are in the situation of if they want a satisfactory EICR they have to agree to the remedial price or get someone to retest, but then they might fail it on something else and they could be potentially be 2 EICR's down for an unsatisfactory certificate.
You could be in the situation of having to pay £100 to the tester for replacing a broken light switch or something as it would be cheaper than another EICR.
 
Hi
If you go behind another electrician who has failed an EICR on something minor, like a couple of broken pendants or something, you carry out the repairs and issue a minor works, the client would then have an unsatisfactory EICR and a minor works cert stating that the C2 items have been rectified.
The original EICR has a 1 month till next inspection date so would these 2 documents together give a OK for 5 years outcome?
Answer is actually no.

the next inspection date is 1 month you cannot change that.

however I think the person carrying out the EICR should have maybe given the full 5 years with unsatisfactory Unless he thought the Istallation was deterio4ating at a rate that it would only last 1 month.

the date originally given for a next date should be on the assumption that the remedial s are carried out Within a month. It states this on the report.
 
could be that whoever done the EICR put 1 month for next test due instead of allowing 1 month for the repairs. what's the date of issue of the EICR?
 
I've wondered about this scenario before.
I've never done this but hypothetically and creatively is there anything to stop you doing another EICR certificate stating:
Purpose "Confirming that remedial works required by inspection on dd/mm/yyyy listed on certificate xxxxxx have been carried out"
Limitations "Limited to checking Supply characteristics, Earthing and Bonding arrangements, that loop tests correlate with previous certificate xxxxx, and remedial works are completed"
Then most items would be LIM unless they were previously coded in which case they'd be a tick. Stick 5 years on it. Satisfactory certificate. Everyone's happy except the customer who's paid for a little bit more time.
Main risk is if original inspector missed something but on other hand the limitation is fairly clear.
Thoughts welcome!
 
I've wondered about this scenario before.
I've never done this but hypothetically and creatively is there anything to stop you doing another EICR certificate stating:
Purpose "Confirming that remedial works required by inspection on dd/mm/yyyy listed on certificate xxxxxx have been carried out"
Limitations "Limited to checking Supply characteristics, Earthing and Bonding arrangements, that loop tests correlate with previous certificate xxxxx, and remedial works are completed"
Then most items would be LIM unless they were previously coded in which case they'd be a tick. Stick 5 years on it. Satisfactory certificate. Everyone's happy except the customer who's paid for a little bit more time.
Main risk is if original inspector missed something but on other hand the limitation is fairly clear.
Thoughts welcome!
That sounds like a very sensible solution - as long as the original certificate passes the 'smell test' that gives the client a piece of paper with Satisfactory on for those who care, and limits your liability nicely.

Anyone who is savvy enough to be able to interpret a certificate should understand what you've done and as long as both certificates are always available it seems like a nice way to comply.

The issue would be with bad EICRS that are done in 20 minutes in order to quote for a new CU. But they would likely be picked up when verifying bonding and supply characteristics as that type of report barely seems to stretch to getting those right even.
 
Just gets to messy juggling diff sparks. Trust thy spark people.


Type into google how much for eicr , says 80 to £150 for 10 way board.
 
Just gets to messy juggling diff sparks. Trust thy spark people.


Type into google how much for eicr , says 80 to £150 for 10 way board.
So if a £150 EICR failed on something like the gas bond had come off the clamp then the tester could charge £100 to reconnect as they know it would be cheaper than getting another EICR as that’s the only way they can get a satisfactory certificate without paying another electrician for another full test.
Everyone just wants page 1 to say satisfactory on an EICR the rest of it could be blank for all they care.
 
So if a £150 EICR failed on something like the gas bond had come off the clamp then the tester could charge £100 to reconnect as they know it would be cheaper than getting another EICR as that’s the only way they can get a satisfactory certificate without paying another electrician for another full test.
Everyone just wants page 1 to say satisfactory on an EICR the rest of it could be blank for all they care.
Just using an EICR for their legislation was a "simple" solution that has caused lots of issues due to poor guidance, the scam artists and the way it was implemented.

I did wonder whether a simple additional list for domestic rental properties created at the time of the original certificate might have some benefits - which lists exactly the remedial work necessary to be carried out (C2s and any C1s that weren't corrected immediately) - Then each item could be ticked/signed as it was done - as long as the entire list is completed, then landlord has complied.

Currently I've seen plenty of EICRs with C2s where it's not immediately obvious what the problem or the solution is, because of poor form filling.

Changing a pendant shouldn't really need the original inspector to come back and re test - and it should also be possible for the landlord to use someone competent in changing pendants (but not maybe in EICRs) to do so. Whereas a CU change obviously needs a higher level of competence, registration etc.

I generally have prior agreement to change fittings as I go if necessary, but obviously that's not always the case.

There would also be issues with that system no doubt, and the "bad" landlords would continue to employ people who pass things incorrectly - but at least it would be a recognised way for letting agents, tenants, and other non electrical people to know what work has to be done.
 
In your dreams
so the first guy done the test certs came unsatisfactory and and all remedial works carried out on any minors , so do you think the persons going to alter the paper work for nowt ,i dont think so . has long has the EICR say satisfactory on it ,but if the the up grade of a consumer unit is replaced the EICR work the paper it was written or tap finger on a lap top.
 
I've wondered about this scenario before.
I've never done this but hypothetically and creatively is there anything to stop you doing another EICR certificate stating:
Purpose "Confirming that remedial works required by inspection on dd/mm/yyyy listed on certificate xxxxxx have been carried out"
Nothing to do with hypotheses or creativity at all: the law does not explicity require EICRs at all.

 
Yes but as a responsible landlord one shall maintain to justify his responsibilities.. if theres a test cert by good spark, if lanlord has proof of guided regulations followed. Happydays have a beeer
 
The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 does not contain either the phrase Electrical Installation Condition Report or the abbreviation EICR.
I agree that you are absolutely correct in this. It just says:
1618694933543.png
The gov.uk guide to the legislation does say the inspection report will usually be an EICR. I know that isn't legally binding, but it does seem fair enough that if the electrical safety standards are defined as BS7671 then one might assume that the testing and inspection details of BS7671 would apply.
1618696367676.png
Unfortunately the reality for landlords isn't aligning with what the law actually says regarding remedial work as letting agencies are turning down "Unsatisfactory" reports even when provided with evidence of rectifications.
That was the background behind my earlier suggestion. It certainly shouldn't be legally necessary to do another report, but it might be the easiest solution for the landlord if a 2nd sparks is doing remedials.
 

The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020​


Under Part 1

interpretation:

2: In these Regulations

“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(5);

And BS7671 chapter 5 is dedicated to show how to fill out the Electrical Safety Certificates.
 
I agree that you are absolutely correct in this. It just says:
View attachment 84779
The gov.uk guide to the legislation does say the inspection report will usually be an EICR. I know that isn't legally binding, but it does seem fair enough that if the electrical safety standards are defined as BS7671 then one might assume that the testing and inspection details of BS7671 would apply.
Absolutely - in reality it will be a (sometimes only allegedly) BS 7671 compliant EICR, just like compliance with Part P invariably means compliance with BS 7671, even though that's not required by law either.

But it's good to be accurate. For example legally there's nothing to stop, say, the Residential Landlords Association from working with one of the schemes to establish a code of practice for safety reporting which is not based on an EICR, and might be better geared to the reality of residential lettings, yet still have due regard to BS 7671. It might usefully have more prescriptive guidance or even rules for coding, so that everybody knows where they stand. It might usefully re-introduce a coding like the old C4 so that every non-compliance isn't forced into some kind of "requires improvement" category. It might want to go beyond BS 7671 in some areas, and decree that no matter what their condition 3036 fuseboards are not permitted, that emergency lighting for escape routes is mandatory, as are interlinked mains powered fire and smoke detectors.

View attachment 84783
Unfortunately the reality for landlords isn't aligning with what the law actually says regarding remedial work as letting agencies are turning down "Unsatisfactory" reports even when provided with evidence of rectifications.
That was the background behind my earlier suggestion. It certainly shouldn't be legally necessary to do another report, but it might be the easiest solution for the landlord if a 2nd sparks is doing remedials.
There's no way that a landlord or agent can have the skills to interpret the combination of an earlier EICR + a later EIC/MEIWC for remedial work.

And is a different electrician who did the remedial work going to want to put his name to a new all-encompassing condition report based partly on the first guy's EICR?

However, (and this is another reason why knowing what it actually says is useful) whatever your views on whether BS 7671 EICRs are mandated or not, the law does not require a second report to be issued after remedial work has been done. The way it is written it is clear that the original report together with written confirmation from a qualified person that the further investigative or remedial work has been carried out is all that's needed. It even says that that combination is what is to be supplied to the tenant and the local authority.

So really it needs both landlords and their agents to be more clued up on what the law actually says, and not just go by commonly repeated misconceptions, and for the former to smack the latter round the head with a rolled up copy if they try to stop the landlord from following a path described in it.
 

The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020​


Under Part 1

interpretation:

2: In these Regulations

“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(5);

And BS7671 chapter 5 is dedicated to show how to fill out the Electrical Safety Certificates.
OTOH BS 7671 does not actually mandate that periodic inspection be carried out.

Chapter 13, Fundamental Principles says that it is recommended that every electrical installation is subjected to periodic inspection and testing in accordance with Chapter 65, and Chapter 65 only applies where periodic inspection and testing is required.

As I said, here and, IIRC, in an earlier thread, in practice of course an EICR is what is going to be done, but we not ought to be blind to the possibility that an alternative might be worked up. After all - if someone builds or renovates a property, the law only requires that they make reasonable provision for safety, not that they comply with BS 7671. And, as you point out, given that the law re rented property says “electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, who's to say that that doesn't mean only compliance with Section 131 and Part 4?
 

Reply to EICR Repairs. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
880
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
898
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
985

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock