This is slightly pedantic, so right up my street.
I'm filling out an EICR. The sockets are wired in 2.5 (apart from some in the kitchen that have been wired in 1mm 3 core and earth. Don't ask...) with a 30 amp 3036 as ocpd.
Forgetting the obvious C2's, the question I have is regarding the Schedule of Test Results. Under the columns that concern ring final continuity results.
Looking at it, the sockets were never wired in a ring. Because of this, would you put N/A in the results section or put >200 (or OPEN). I have already noted undersized cabling on the certificate. I warned you it was pedantic!

On a further note, just letting you know, it's a 3rd Floor flat. Ze is 187 ohms. TNC-S. On reconnecting the gas bond it changes to 0.21 ohms. And all those pesky little earth wires supplying class 1 lights and switches have been cut off. I must admit, they do tend to get in the way and everything works fine without them. Also saves having to change the wire in a 3036 when there's a live to earth fault I suppose.
 
Sounds like a rather joyous EICR all around.
Finding a Ze like that is strangely satisfying, telling the customer that the gas changing their supply to plastic would make their electrics lethal might possibly help them see the value of these inspections.
It would be interesting to hear how you get on with the DNO...

I'm also a bit intrigued, was there a PME sticker?
 
Sounds like a rather joyous EICR all around.
Finding a Ze like that is strangely satisfying, telling the customer that the gas changing their supply to plastic would make their electrics lethal might possibly help them see the value of these inspections.
It would be interesting to hear how you get on with the DNO...

I'm also a bit intrigued, was there a PME sticker?
Yes, it was a bundle of laughs. On the Observations and Recommendations I got up to 27 items. Could have done more, but got fed up.

Luckily unoccupied flat for rental.

PME sticker in ground floor mains room. Ze at origin 0.13 ohms
 

Reply to EICR test results schedule in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
674
I trained as a electrician in the 70s but have long since retired. Just had an EICR test done on my property in advance of selling. I have a 60s...
Replies
25
Views
2K
Folks it seems that we now have Issue 7 of the BPG#4 on EICR. Trying to compare them shows only minor changes, but those of note are: Page 9...
Replies
19
Views
1K
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
959

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock