Discuss EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Doing an eicr on transport company's yard,most probably 15 years+, old.
Normal observations,wondering what you guys think about this one,in the middle of nowhere there are 3p/N/E commando plug/ sockets,rated 32amps,these are used for charging refrigerator units,supplied with trailing leads.
They are cabled undergrd by swa cabling,to a 4 pole rccd 30 ma,this is from a DB 32amp 3p MCb.using the sheath as earth & PME From the DB For its earth ,anyone see any probs.
 
what regulation do you think it contravenes? and what's the csa of the swa?
 
i see your point, as that installation is similar to car charging points in that you are charging equipment on metal vehicles. i'd be glad to hear the views of other members on this one.
 
I don't see a problem, the power to these trucks is not for use as a habitable environment. I have tested many a site with the same set up and made no comment.
 
I would have said that the potential for a risk is present, however the power supply for the refrigeration unit should be entirely insulated from the vehicle wiring and so the chance of there being an exposed conductive part of the 3 phase installation that is accessible to touch when charging the units would seem to be very small.
Ideally a TT earthing system could be employed effectively here but a risk assessment may well conclude that it is not required to reduce the risk of perceived shock.
However you have seen the installation and would be best placed to make that judgement.
 
Thanks,it's been like that when originally installed,bit of a nightmare to actually TT the system,but will note my concerns.
I'm afraid it's the same old installation problems we find,leaving it as it was.
Swa's installed & using the sheath for both earth & main bonding,& near impossible to correct now,but for my conscience I will note,& then up to my superiors to decide.
 
Oh dear, if bonding is wrong too I would like to see that addressed before any further work. Is that being too harsh?
 
Oh dear, if bonding is wrong too I would like to see that addressed before any further work. Is that being too harsh?
No ,that's my opinion to,just noting what's gone wrong over a period of years,& see what happens.
I really can't see any change in the installation happening though,cabling all underground & a long way away from main intake.Thanks anyway.
 
What's your views on,while doing this report,finding swa's are being used for main & bonding conductors.A sub main from intake cabinet,on a tncs system,35mm 4 core swa to a TPN DB.
The swa is connected to the Db,& a link from banjo to the MET.
A earth conductor then connected to a structural steel frame building,then another to a water pipe etc.
To use this earthing system,a bonding conductor sized correctly should be used.
Near impossible to get this sorted now,the yard been like this for over 15 years.
 
Hi Cliffed, to clarify - the 4 core 35mm SWA is used to extend the 3 phase service from the TNCS PME DNO cutout. There are no connections to the cutout except via this SWA, so the armour is providing CPC for the SWA and earthing conductor function for the site?

4 core 35mm SWA has steel of 84mm and resistivity ratio given as 8.5 on p60 of GN8 meaning equivalent to 9.88mm of copper. Which means its undersized for current regs, which I think will be 10 or 16 from Table 54.8 (depends on incoming DNO neutral size).

I'm not familiar enough to know if it was sized ok for an earlier edition? In which case it could be a C3 improvement?
 
Exactly right,the actual incoming neutral size is 240 mm,which I think gives a Earth bonding conductor of 50 mm.
Interesting to know the C3 code given
 
Hi Cliffed, to clarify - the 4 core 35mm SWA is used to extend the 3 phase service from the TNCS PME DNO cutout. There are no connections to the cutout except via this SWA, so the armour is providing CPC for the SWA and earthing conductor function for the site?

4 core 35mm SWA has steel of 84mm and resistivity ratio given as 8.5 on p60 of GN8 meaning equivalent to 9.88mm of copper. Which means its undersized for current regs, which I think will be 10 or 16 from Table 54.8 (depends on incoming DNO neutral size).

I'm not familiar enough to know if it was sized ok for an earlier edition? In which case it could be a C3 improvement?
I thought the ratio was 8, not at home to check.
 

Reply to EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
541
Hi guys, This has probably been asked many times before but just want to know others opinions. Just done an EICR and have found (or not found) any...
Replies
8
Views
4K
Hi everyone, firstly hope you all had a great New Year. Wanted to get everyone’s thoughts on best design for Zappy EV charging point install...
Replies
8
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock