My company has recently done some air source heatpumps which require DNO notification and EV chargers which also require DNO notification. On an EICR today came across a 14.4kW electric boiler on a 60A supply (installed last year by others). Apart from the obvious issues I looked into whether these should also be notified to DNO but everything I find seems to suggest electric boilers do not need to be notified, even though they can be 2x load of EV point!
Does anyone know if this is correct?
 
My company has recently done some air source heatpumps which require DNO notification and EV chargers which also require DNO notification. On an EICR today came across a 14.4kW electric boiler on a 60A supply (installed last year by others). Apart from the obvious issues I looked into whether these should also be notified to DNO but everything I find seems to suggest electric boilers do not need to be notified, even though they can be 2x load of EV point!
Does anyone know if this is correct?
Basically no they don't but :You must notify your local DNO if you make any significant change to your connection, such as installing one of the following energy devices:


  • solar photovoltaic (PV)
  • heat pump
  • electric vehicle (EV) charge point
  • battery storage

 
I was aware of those, even gov.uk website specifies those. I know what your suggesting is that it is a significant alteration but the DNO form has no section for anything other than PV, EV, Heat pump or batt. storage. It seems strange electric boilers are not listed given their potential current draw and extended periods of use.
 
I was aware of those, even gov.uk website specifies those. I know what your suggesting is that it is a significant alteration but the DNO form has no section for anything other than PV, EV, Heat pump or batt. storage. It seems strange electric boilers are not listed given their potential current draw and extended periods of use.

It's left to the electrician to decide, after all he's the one responsible for the design and installation and i suppose upto him whether to phone the dno and for them to say no :)
 
Last edited:
Do you mean a incoming 60A supply or a 60A circuit to the boiler? I've seen a 50A distribution circuit and a 40A shower, 32A Hob, 32A Cooker and 4x32A sockets ++ etc on a 60A head

ASHP's are basically a pump and a fan, they aren't large equipment, and if your PV is less than 16a per phase the DNO just needs a form filled within 28 days
 
Do you mean a incoming 60A supply or a 60A circuit to the boiler? I've seen a 50A distribution circuit and a 40A shower, 32A Hob, 32A Cooker and 4x32A sockets ++ etc on a 60A head

ASHP's are basically a pump and a fan, they aren't large equipment, and if your PV is less than 16a per phase the DNO just needs a form filled within 28 days
The cutout is 60A, boiler rated at 14.4kW which is 62.6A but supply circuit is 40A MCB. I don't know if there is some way to limit max output on the boiler in the settings as 40A MCB seems to be holding. We didn't install so no idea how it's been set up. But there is also induction hob and oven in there as well.
Maybe the service fuse has been replaced with a section of galv conduit!
 
The cutout is 60A, boiler rated at 14.4kW which is 62.6A but supply circuit is 40A MCB. I don't know if there is some way to limit max output on the boiler in the settings as 40A MCB seems to be holding. We didn't install so no idea how it's been set up. But there is also induction hob and oven in there as well.
Maybe the service fuse has been replaced with a section of galv conduit!
If you look back at the time current graphs for a type B 40A MCB, the trip time at 62.6A is apparently a long shower or the time taken to boil a hot water tank.
 
I don't know if there is some way to limit max output on the boiler in the settings
A lot of electric boilers have multiple elements, it's usually just a matter of unplugging one of them. Most ramp up by switching the elements on in sequence depending on the demand required, unplug the last stage. The last 2 I wired all had the 6th stage disconnected at the factory, the element and live wiring was there, just not connected to meet the rating plate of that model.
 
A lot of electric boilers have multiple elements, it's usually just a matter of unplugging one of them. Most ramp up by switching the elements on in sequence depending on the demand required, unplug the last stage. The last 2 I wired all had the 6th stage disconnected at the factory, the element and live wiring was there, just not connected to meet the rating plate of that model.
Thanks. I suspected that might be the case, was aware a 40A MCB would take an overload of full 14kW load for a few minutes or so, but apparently its been fine, MCB isolated circuit ok so no welded contacts. We were there to do EICR so not going to start stripping down electric boiler to satisfy our curiosity!
 

Reply to Electric boilers and DNO notification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
745
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
498
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock