RubberyChicken

Hi guys,

I've not long been moved into my new house and this morning whilst running the shower I noticed an awful smell coming from the shower box. After opening up the shower, this is what I found (please see picture). Anybody know why this has happened and how I can prevent it from happening again? ImageUploadedByTapatalk1373197205.261248.jpg
 
This is the result of a poor termination (loose connection) this in turn has led to overheating of the poor connection hence the results.... the extent of the damage to the supply cable and the internal wiring needs checking to see if this is a simple fix or requires replacement of some of the cable.

This will need to assessed by someone who is expeienced and competent.

I recommend an Electrician takes a look and furthermore they can assess this is solely down to a loose connection or whether other factors have played a part like correct cable size etc.
 
9.6kW just about on limit for 6mm as long as it's not smothered in itchy crap.
 
Unlikely that the supply cable will have enough slack in it to reterminate anyway, looking at that picture. DIY install for sure. Would definitely get an electrician in to assess the situation with this one.
 
i'd say that's a 6mm cable, judging by the cpc - a 10mm t&e cpc would be stranded.

the shower looks like it's 9.5kw which is pushing it for a 6mill cable (depending on circuit length & installation method).
 
Is it actually possible that that cable is 4mm? I has one of these last year, 9.5kw shower on 4mm. And the cable was run in insulation.
 

Reply to Electric Shower Problem in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
965
Just had an electric shower installed. Electrician put the wire in low so the unit is at waist height when stood in the shower enclosure. Is this...
Replies
24
Views
3K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock