Looking for some advice please. I have lived in my property for almost 7 years now. Since living here every 6 months my heating element blows in my fan oven. I have purchased 3 new cookers since living here all different models. Instead of replacing the oven I started getting the element fixed purchasing directly from the oven manufacturer and getting an electrician in.
I live in a council property and the council have been out to ‘check’ my electricals and said they’re isn’t a fault anywhere they can find. It trips all of my electrics when it goes, my lights occasionally also trips the electrics out and my plug sockets.
Surely there is a fault somewhere?
Thankyou in advance 😊
 
I am making some assumptions here so bear with me.

assumptions,
1. You are houseproud and like to keep a clean oven
2. It is a fan oven
3. you prefer to use a spray on oven cleaner or even an aerosol
4. you make sure that you spray the back of the oven well so all the grime "melts off"

This is what MAY BE HAPPENING

When you spray the back of the oven, you are spraying a caustic cleaner (similar to acidic but not quite the same) some of it goes through the circular vent holes in the middle of the oven.

when that happens, some of it drips on the fan and the fan element, many oven cleaners will eat through the outer case of a heater element as they are not designed to be in contact with caustic cleaners.

the cleaners remain caustic even when dry and as soon as a small amount of moisture is let into the oven, the caustic cleaner will become active again and start eating away at the elements outer case.

unfortunately, the best way to avoid this is simply to avoid the "spray on wonder clean products" especially at the rear of the oven and use a non aggressive cleaner like washing up liquid and some harder scrubbing.
 

Reply to Electrical fault cooker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
651
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
743
I have just replaced my old double oven which was about 10 years old with a new model as whenever I used the top oven it tripped the electrics...
Replies
1
Views
599
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
749
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock