Discuss Electrical supply advice and other queries in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
1
Hello all. I have been asked to install some AC 3 phase units totalling 362amps. This is only the power required for the ac units and not the ancillary things. Is lights, sockets and other things,,). Since my experience is very limited I'm anything above three phase 100amps, I would be grateful for some advice.

My questions are as follows:
What type of supply would I need, apparently above 200amps, I have to have a transformer dedicated transformer. Is this correct.

The supply side sizes. 200 400 600 1000 or can I decide the supply I need.

Is there anything like Diversity I have to factor in or discrimination.

Thank you got your time
All advice will be appreciated
 
Are you in Birmingham, uk?

You might be able to get a big enough supply at 400v for your requirements but first we need to find out what you actually require.
 
You need to determine the exact supply requirements, and then approach the dno for a new/upgrade supply.

At that rating they will likely have questions such as peak current (is it a big motor - with substantial starting current, or is it a large accumulation of small loads with negligible increase when energised etc).

They will then provide a cost, which may be just a new feed cable, or a complete circuit depending upon their capacity at that point.

In an industrial/commercial setting that isn't a big demand, but is outwith that.

This is for the uk?

For really big loads ( or somewhat smaller in remote locations), it is normal to connect at 11kV, in which case you can use private companies to install, doesn't have to be the dno.

In saying that, this looks far to small to bother with that sort of contestable type work
 
Hello all. I have been asked to install some AC 3 phase units totalling 362amps. This is only the power required for the ac units and not the ancillary things. Is lights, sockets and other things,,). Since my experience is very limited I'm anything above three phase 100amps, I would be grateful for some advice.

My questions are as follows:
What type of supply would I need, apparently above 200amps, I have to have a transformer dedicated transformer. Is this correct.

The supply side sizes. 200 400 600 1000 or can I decide the supply I need.

Is there anything like Diversity I have to factor in or discrimination.

Thank you got your time
All advice will be appreciated
You will need a new transformer. The existing 3x100 35mmsq feeding the cut outs are far too small. The DNO will require your maximum demand. As there are motors, extra allowance will need to be made. Only you know the answer to that. Come back to us and I/we will calculate for you.
Regards, UKPN⚡
 

Reply to Electrical supply advice and other queries in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
734
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
616
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
703
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
646
Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock