Discuss Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
emergency lights not coming on when breaker is switched off, are these wired just for use as normal lights rather than emergency??? Sorry not done much emergency lights before

AFCAC741-D30C-467D-AF14-1FCA248CBB91.jpeg


D323798B-1783-45F9-A656-4DD969CD38DF.jpeg
 
The lamp holder's not even connected to the battery pack.
 
the wiring looks correct to me,
I presume its a 2D style led panel that is attached. the 4 coloured singles go direct to the led's as a low voltage supply when the mains fails.
have you checked that you get power between N and L1 (next to the earth) at all times and that the power drops out when the breaker is off?
 
the wiring looks correct to me,
I presume its a 2D style led panel that is attached. the 4 coloured singles go direct to the led's as a low voltage supply when the mains fails.
have you checked that you get power between N and L1 (next to the earth) at all times and that the power drops out when the breaker is off?
Yes turn breaker off and no power there
 
it looks like a combined battery and charger unit, I suspect the battery has failed, if its being powered up correctly I would expect a tell tale led to show on the surface of the lamp somewhere (possibly a green led)
when you remove the power, the tell tale lamp should go off and the light normally comes on at half brightness until the battery is flat.

Edit, just zoomed in on picture, confirming the detail above.
 
Last edited:
Does the indicator light work to show the battery is charging?
Just make sure that the internal battery is properly connected in the emergency pack as they can be a bit finicky
 
New posts

Reply to Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi folks, Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units. I have...
Replies
2
Views
496
Morning Needing help regarding Ansell AARDRINA/DD1/SM3. I’ve installed 6 in one room, one being an emergency light fitting. All 5 standard...
Replies
15
Views
452
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock