Discuss Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net

it looks like a combined battery and charger unit, I suspect the battery has failed, if its being powered up correctly I would expect a tell tale led to show on the surface of the lamp somewhere (possibly a green led)
when you remove the power, the tell tale lamp should go off and the light normally comes on at half brightness until the battery is flat.

Edit, just zoomed in on picture, confirming the detail above.
Yes once power is on the green light comes on, which I presume means it’s charging
 
Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
 
Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
So at the min the lights are switched by photocell and come on at night so the batteries should be charged and test mode does nothing
 

Reply to Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi folks, Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units. I have...
Replies
2
Views
495
Morning Needing help regarding Ansell AARDRINA/DD1/SM3. I’ve installed 6 in one room, one being an emergency light fitting. All 5 standard...
Replies
15
Views
447
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock