Hi i mostly do commercial so not 100% up todate on the regs.

My mate wants me to wire up a ensuite for him. There is no bath or shower so im under the impression there are limited restrictions as there are no zones.

I am putting in two fused spurs and a down light.

Aslong as the spurs are rcd protected is this ok to do?

Cheers
 
is it just a bog and basin then? if so, it's not a special location, therefore RCD protection is only required for sockets and cables buried in walls ( 522.6.101 ).
 

Reply to En suites - Regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

i am wiring up a new en-suite: it is about 1.7m square, shower cubicle in one corner, toilet in other, door between, basin next to shower. I will...
Replies
2
Views
686
Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
1K
Scenario... 2 x switched fused spurs located in a shower room. They are 610mm from side of shower, so outside zones. However, they could still...
Replies
6
Views
1K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock