Hello Katie.
Tell your husband not to touch it. There is almost certainly high energy present (arc flash hazard); it should have been risk-assessed and labelled as such. If so, that means arc-rated PPE is essential to safely operate this circuit breaker. The lack of arc flash labelling and circuit designation labels leads me to think it has not been maintained. If the site owner does not know how to operate it, it may not have been functioned for an unknown period of time and may be unsafe. Call the DNO; they have all the right PPE to deal with it and will also be able to service and test it, which will be required. It then needs to go on a routine maintenance schedule and be risk-assessed for the potential arc flash hazard. And, usually, the lower the service voltage, the greater the arc flash hazard, so don't relax if it's found to be "only" 415 volts. Keep well away from it in the interim.
Regards,
Colin Jenkins.