Discuss EV chargers and double pole RCD's. in the UK Electrical Forum area at ElectriciansForums.net

goasis

-
Esteemed
Reaction score
400
So regulation 722.531.3.1 says RCD's shall disconnect all live conductors.
Is this requirement met if the charger itself contains a DP RCD? As presumably there is no reason that the installed circuit requires a DP RCD? in fact depending on cable type and install methods the cable may not need an RCD at all?
 
So regulation 722.531.3.1 says RCD's shall disconnect all live conductors.
Is this requirement met if the charger itself contains a DP RCD? As presumably there is no reason that the installed circuit requires a DP RCD? in fact depending on cable type and install methods the cable may not need an RCD at all?
Bit of a interpretation required, the rcds in the chargers are often rcds as in 61008/61009 but rdc-dd devices which are without checking are a different standard 62955 or similar.
Easee have an issue at present with swedish authorities about this.

Given the charger is a radial circuit with one device fit an upfront type a double pole and you avoid any doubt, Myenergi recommend it as do a lot of manufacturers regardless of what is inside the unit. Wouldnt cause any wider inconvenience even with lack of selectivity as its the one device.

Depending on cable and route you might need upfront rcd protection anyway
 
Bit of a interpretation required, the rcds in the chargers are often rcds as in 61008/61009 but rdc-dd devices which are without checking are a different standard 62955 or similar.
Easee have an issue at present with swedish authorities about this.

Given the charger is a radial circuit with one device fit an upfront type a double pole and you avoid any doubt, Myenergi recommend it as do a lot of manufacturers regardless of what is inside the unit. Wouldnt cause any wider inconvenience even with lack of selectivity as its the one device.

Depending on cable and route you might need upfront rcd protection anyway


cheers, yes i agree with what you are saying, and an RCD is required for the cable/route. The issue is a Scolmore Elucian board has been fitted and their RCBO's are single pole. Which seems massively shortsighted. (both from a manufacturing point of view, and a installation design point of view)
 
cheers, yes i agree with what you are saying, and an RCD is required for the cable/route. The issue is a Scolmore Elucian board has been fitted and their RCBO's are single pole. Which seems massively shortsighted. (both from a manufacturing point of view, and a installation design point of view)
fit an MCB in the board then small 2 module enclosure adjacent and route the ev charger circuit through a double pole type a rcd. job done
 
cheers, yes i agree with what you are saying, and an RCD is required for the cable/route. The issue is a Scolmore Elucian board has been fitted and their RCBO's are single pole. Which seems massively shortsighted. (both from a manufacturing point of view, and a installation design point of view)
Scolmore Elucian aren’t a manufacturer, they’re an importer/supplier of products, pretty much like Fusebox.

They have little or no design input into the product and they have little or no experience of selection. They get what they get given by the agents in China and join the race to bottom on price and quality.
 
Scolmore Elucian aren’t a manufacturer, they’re an importer/supplier of products, pretty much like Fusebox.

They have little or no design input into the product and they have little or no experience of selection. They get what they get given by the agents in China and join the race to bottom on price and quality.
I think Scolmore would disagree with this statement, being a British designer and manufacturer of electrical products.
The same is true of CP Fusebox.
 
fit an MCB in the board then small 2 module enclosure adjacent and route the ev charger circuit through a double pole type a rcd. job done
Always worth considering, also it allows a far wider range of MCB and RCD characteristics to be achieved (i.e. beyond Type A with B/C curve over-current).
 
I think Scolmore would disagree with this statement, being a British designer and manufacturer of electrical products.
The same is true of CP Fusebox.
CP Fusebox has just been sold to a lighting company. They had 8 employees and sold via agents. They’re an importer of mass produced Chinese manufactured consumer units. Excellent marketing by them though tbf.

If they were called CP Electrical consumer units, nobody would touch them.

Scolmore are definitely not a manufacturer, their annual accounts explain what are. An importer and supplier of electrical equipment. If they were a British designer and manufacturer, why would they manufacture an RCBO that doesn’t help them comply with latest regulations?
 
This is what Scolmore claims to be:

"Today, the company operates from its purpose-built 150,000sq ft. Head Office and Distribution Centre – still in Tamworth - where it designs, develops and manufactures an ever-expanding product range for distribution throughout the UK and worldwide."
 
CP Fusebox has just been sold to a lighting company. They had 8 employees and sold via agents. They’re an importer of mass produced Chinese manufactured consumer units. Excellent marketing by them though tbf.

If they were called CP Electrical consumer units, nobody would touch them.

Scolmore are definitely not a manufacturer, their annual accounts explain what are. An importer and supplier of electrical equipment. If they were a British designer and manufacturer, why would they manufacture an RCBO that doesn’t help them comply with latest regulations?

So you are saying that Scolmore do not manufacture in the UK?
 

Reply to EV chargers and double pole RCD's. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
843
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
582
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock