I came across this today when changing a shower isolator that was stuck in the on postition.

40A Hager RCBO feeding 10mm² twin + earth to a pull cord shower isolator. On the load side of the isolator there was 10mm² going off to the shower as you would expect, but also from the isolator was 2.5mm² T+E feeding a 3A fused spur in the loft, which then fed an extractor via 1.5mm² T+E.

So the extractor is switched on and off with the isolator, along with power to the shower. Not very good practice IMO, but is it compliant?

I believe so: the 2.5mm² and 1.5mm² T+E should be protected from overload by the 3A fuse. PFC was about 1100A, so the requirements of the adiabatic equation should be met. RCD protection means disconnection times are met.

What do you guys and girls think?
 
My biggest concern is that the fused spur is in the loft and may not be accessible.
 
Switches and protective devices should be accessible.
Partly for safety to turn off in emergency
Mainly for convenience though.
 
Don't see an issue really, just a bit unusual, I have come across this before, my own house has underfloor heating in an en-suite shower that is fcu'd off the shower itself.

Got busy with my calculator when I found out, everything was ok disconnection times, adiabatics etc

There is the issue of circuits not being as independent as I would have liked, but other than that...
 
I hadn't considered that. Actually one of the better lofts I've been in - loft ladder, boarded out, and with a light. But you think it would be a reg breaker had it been under 12" of itchy stuff?
The insulation is, nt an issue as both the 2.5 and 1.5 will never be carrying more than the fan load. The 3 amp fuse is well below what the regs allow for cables of those sizes embedded in insulation. In practice however it would be better to connect the fan to the light. I personally like to wire the fan back to the switch and allow the customer the option of switching the fan separately
 
The insulation is, nt an issue as both the 2.5 and 1.5 will never be carrying more than the fan load. The 3 amp fuse is well below what the regs allow for cables of those sizes embedded in insulation. In practice however it would be better to connect the fan to the light. I personally like to wire the fan back to the switch and allow the customer the option of switching the fan separately
They will under fault conditions prior to the spur.
 
The problem I see is that the extractor is being switched on and off, probably every day, by use of the shower isolator. The isolator should not be used like this.
 
Sounds to me that the prisable is a good idea .The main time you need the fan on is when the shower is on . If there is a window in the room you would not need the light on to have a shower, so if the fan was controlled by the light switch it may not be used. Much better that the fan comes on when the shower is in use. I have seen similar sets up with cooker extract fans connected to the outgoing side of a cooker switch. So the fan comes on when the cooker is turned on.
 
Sounds to me that the prisable is a good idea .The main time you need the fan on is when the shower is on . If there is a window in the room you would not need the light on to have a shower, so if the fan was controlled by the light switch it may not be used. Much better that the fan comes on when the shower is in use. I have seen similar sets up with cooker extract fans connected to the outgoing side of a cooker switch. So the fan comes on when the cooker is turned on.

But the shower isolator shouldn't be used as a functional switch for the fan.
 

It will have a lot of wear and tear with daily use. And some fan isolators aren't the most reliable of things at the best of times. I would normally recommend people isolate the shower every time they have used it. Also the fan could do with leaving on for a few minutes after the shower has been used,
 
It will have a lot of wear and tear with daily use. And some fan isolators aren't the most reliable of things at the best of times. I would normally recommend people isolate the shower every time they have used it. Also the fan could do with leaving on for a few minutes after the shower has been used,
Extractor fans have a duel function in most bathrooms. Moisture and odour removal. A switchwire to the light switch covers all these options
[automerge]1599648895[/automerge]
But the shower isolator shouldn't be used as a functional switch for the fan.
Correct. The shower switch is first and foremost a means of isolation for any service personnel working on the shower
 
Extractor fans have a duel function in most bathrooms. Moisture and odour removal. A switchwire to the light switch covers all these options

Indeed. Although it means you always have to switch the light on when you want the fan on. Even if it's daylight.

I still like the 'old fashioned ' fan with built in pull cord. If you want the light on then switch the light on, if you want the fan on then switch the fan on. I like a simple life!
 
Indeed. Although it means you always have to switch the light on when you want the fan on. Even if it's daylight.

I still like the 'old fashioned ' fan with built in pull cord. If you want the light on then switch the light on, if you want the fan on then switch the fan on. I like a simple life!
Ageed.Thats always a good option. But that's why I wire the switchwire for the fan back to the light switch. If homeowner requires a separate switch for fan just install a 2 gang switch. Bang. Done. In reality here everyone has a mirror light as well as a centre light so it's nearly always possible to have a light on without having to switch on the fan anyway.
 
It will have a lot of wear and tear with daily use. And some fan isolators aren't the most reliable of things at the best of times. I would normally recommend people isolate the shower every time they have used it. Also the fan could do with leaving on for a few minutes after the shower has been used,

Just realised my post said 'would' instead of wouldnt! To clarify, I WOULDN'T recommend people operate the shower isolator after every shower.
 

Reply to Extractor fan from shower isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
378
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
250
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
434
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock