Discuss Farm Installation help in the UK Electrical Forum area at ElectriciansForums.net

W

Welshsparky

Hi all

Went to look at a job today on a farm , 3 phase board with 75mm supply on a 100 amp 100 ma rcd mainswitch, with a submains out to the house , which is also protected by another 100 ma rcd, problem is every time theirs a trip in the house it trips at the main distribution board also which is situated in a barn, What would be the best way to rectify this? would it be possible to swop the domestic consumer unit for 30ma dual rcd, and change the mainswitch at the incomer for a 100 ma time delay?
 
One upstream RCD to protect an entire estate is never a good idea. You need to think about some proper cascading discrimination which will no doubt make use of time delay RCD's at some point.
 
Are you saying that you can not guarantee discrimination with a 100mA non-time delay RCD at main supply feeding a sub board with a 30mA non-time delay RCD? In other words, its is only time delay that can provide adequate discrimination, and not 100mA vs 30mA RCDs?
 
Are you saying that you can not guarantee discrimination with a 100mA non-time delay RCD at main supply feeding a sub board with a 30mA non-time delay RCD? In other words, its is only time delay that can provide adequate discrimination, and not 100mA vs 30mA RCDs?

Thats right, it's pot luck which one trips first if you don't have a time delay.

Welshsparky, I'm guessing that it's a TT supply which is why you have a main switch 100a/100mA?
 
Yes its a TT, i think ill have to go for the time delay RCD mainswitch, problem being customer has had a celler conversion, If the pumps are knocked off for more than 20 minutes it could potentially flood the cellar argh!
 
Well to my knowledge there isn't any such 75mm cable, so i'm taking this as a typo error!! My guess for a 3 x 100A supply is 3 x 25mm conductors!!! lolAs

been previously suggested, this installation needs a 300mA S type at the origin, that will discriminate with any 100mA RCDs downstream. I would also suggest that being a TT system, any CU should be all 30mA RCBO protected rather than split or single RCD protected CU's....
 

Reply to Farm Installation help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock