Hi..... just a quick question i have regarding RCD on TT systems, would you class the RCD,S as just fault protection, or additional protection aswell?

i am an apprentice doing the proper route, 2357 and was having this discussion today. any help would be greatly appreciated.

Thanks simon.
 
if your Zs readings are higher thasn the max. values given in BS7671, then the RCD/s are classed as fault protection as well as additional protection. max. Zs for all circuits is then 1667ohms ( assuming a 30mA RCD)
 
Say it was just a split load board with x2 30ma rcd,s

Then if i had an upfront 100ma s type would that be additional protection?

Thanks simon
Very good question M8, I would suggest if the main switch in the DB was a 100 ma S type and then you had a split 30 ma rcd on both sides of the split then it would be additional protection, you have the usual 30ma with a back up 100 ma S type, definitely additional.
 
posted same time. your 30mA RCDs are additional. the 100mA is fault protection. but either or both 30mA RCDs would probably trip first in the event of a fault.
 
yep, it's just ohms law. look at table 41.5 in bgb.
 
Cheers, we dont seem to have gone in to much depth on TT systems at college and i have worked on a few since i started so just want to make sure my knowledge is up to scratch when dealing with this earthing arrangement.

thanks simon
 
On a TT system if you're unable to achieve a TN vaule for your Ra and you are utilising automatic disconnection of supply as the sole protective measure then you must rely on an RCD for fault protection. This can be an RCD of any rating (you are not limited to 30mA) depending on your Ra value and its stability. If however you choose a 30mA RCD to provide that fault protection then it is also providing additional protection because of its 30mA rating. Remember, only a 30mA RCD can be used as additional protection, any other rating (100mA, 300mA etc...) will not provide this.

The decision as to whether or not to provide an up front type-S RCD is one that is completely up to the designer. On a TT system, an up front time delayed RCD will not provide additional protection as they are typically rated at 100mA or more, neither will it provide fault protection for a final circuit as it wil not trip within the required time of 0.2s. A type-S RCD can only be used to provide fault protection to distribution circuits that require a maximum disconnection time of 1s (on a TT system that is) although some people, myself included, like to fit them as 'back up' (a term not defined in BS 7671) protection. In other words, if an RCD fails to operate on one or more final circuits then the type-S will provide disconnection... eventually. Bear in mind however that you are only required to protect against single fault conditions, therefore the installation of an up front time delayed RCD is not always mandatory. In a typical domestic TT installation 99% of the time you will not be required to install a type-S, although like I and others have said, it is highly advised.
 
Last edited:
On a TT system if you're unable to achieve a TN vaule for your Ra and you are utilising automatic disconnection of supply as the sole protective measure then you must rely on an RCD for fault protection. This can be an RCD of any rating (you are not limited to 30mA) depending on your Ra value and its stability. If however you choose a 30mA RCD to provide that fault protection then it is also providing additional protection because of its 30mA rating. Remember, only a 30mA RCD can be used as additional protection, any other rating (100mA, 300mA etc...) will not provide this.

The decision as to whether or not to provide an up front type-S RCD is one that is completely up to the designer. On a TT system, an up front time delayed RCD will not provide additional protection as they are typically rated at 100mA or more, neither will it provide fault protection for a final circuit as it wil not trip within the required time of 0.2s. A type-S RCD can only be used to provide fault protection to distribution circuits that require a maximum disconnection time of 1s (on a TT system that is) although some people, myself included, like to fit them as 'back up' (a term not defined in BS 7671) protection. In other words, if an RCD fails to operate on one or more final circuits then the type-S will provide disconnection... eventually. Bear in mind however that you are only required to protect against single fault conditions, therefore the installation of an up front time delayed RCD is not always mandatory. In a typical domestic TT installation 99% of the time you will not be required to install a type-S, although like I and others have said, it is highly advised.

Not a lot of people know that...............me included:)
Brilliant mate............great stuff.
 

Reply to Fault protection/additional protection. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
760
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
922
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
470
Hi , Wondered if anyone can help , i currently install and test Trace Heating Cable on Mechanical Pipework for Frost protection . Recently our...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock