Discuss Faulty Danfoss 12 v fridge in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
2
I have a Cubigel GD30fc compressor fridge which is a BD35 Danfoss with different connections on the control box, It only runs if I link out the thermostat, the compressor gets hot but there is no cooling, the fault code LED just shows a continuous light.

I'm out of ideas. Is there any check I can do for loss of gas ?
 
There's no definitive test you can do to know if it's short of gas without putting guages on the system. Gas leak and internal blockage problems can show similar external symptoms. You can visually check for oil marks or stains because wherever there's a gas leak there will be some oil also leaked. Sometimes you can see an oil stain at the point where there's a gas leak but sometimes it's not that obvious either. If it has a very slow leak over time there might be a damp looking dirt patch at the site of the leak where dust and debris has stuck to the oil.
 
In addition, just because the compressor is running doesn't mean it's compressing. Could be a faulty reed for example.

So you are probably best to get a refrigeration specialist in, who will have all the gear, and the knowledge, to be able to diagnose/repair it.
 

Reply to Faulty Danfoss 12 v fridge in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, I have been having issues with our fridge causing my modem and video card on my pc to drop out. -They are on the same ring circuit, have...
Replies
8
Views
796
Hello all, I am a Design and Technology student completing my final project of a portable solar-powered esky/mini fridge cooling system, however...
Replies
0
Views
748
Im trying to make a Star Wars Prop for a course project where the dealine is comming up very fast in days and I need to do the report so really...
Replies
0
Views
374
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock