Discuss Faulty external lights Help Needed in the UK Electrical Forum area at ElectriciansForums.net

dlt27

-
Reaction score
26
Hi All, thanks for any advice.
I fitted some spike lights about 12 months ago in a customers garden and also some in my own (14 in total). Last October customer phoned to say lights were tripping RCD and when I investigated it turned into a nightmare. It was my fault partly because I made SWA off into resin joint and flexed light out of resin joint as well to stop any water ingress ( now use adaptable boxes and gel), however a days labour lost later and resin joints cut off I found out the flex on the spike lights was down not the fittings. I fitted 2 new spike lights and all was ok.
Since sorting the customer has had exactly the same happen again with another circuit that has spike lights on and also mine have done the same , I cut every flex of mine and every one is showing a really low reading. Seems like cable is absorbing water or something.
I have googled the problem and also found others have had the same thing happen.
The problem I've got is what to replace them with! I've brought two from rexel different make (enlite), but they have exactly the same flex ( Chinese rubber cable beginning with X) installed as faulty ones I got off internet.
I was wondering if anybody had had the same problem and also has anyone got any ideas what else I could use?
I thought about mini floods on a spike, but thought might look a bit rubbish.
Greatly appreciated if anyone can recommend anything.
 

Reply to Faulty external lights Help Needed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
682
I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
337
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
670
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock