I have bathroom gfci circuit with two gfci in series, the down stream tripped wouldn't reset. Found line potential on both the neutral and hot wire. Further investigation found the up stream unit failed. Has anyone else ever seen this problem. Also the upstream gfci wasn't tripping.
 
It sounds like the upstream GFCI might have been open-circuit in the neutral pole or lost its neutral connection from the panel. That could cause the neutral on the output side to appear hot, a condition which might prevent the downstream unit being reset, as some designs test for the correct relationship between hot, neutral and ground and trip if abnormal.
 

Reply to Faulty gfci in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a small power washer with a two-wire cord and GFCI plug. My outdoor and garage receptacles are on a "house GFCI" circuit, wired in series...
Replies
2
Views
2K
Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old...
Replies
5
Views
805
A 13-year-old GFCI kitchen receptacle went bad, so I replaced it with a new one I bought from Lowe's (Eaton model TWRSGF20). After one day, this...
Replies
4
Views
1K
Upfront disclosure, I am a DIY homeowner with basic knowledge of electrical safety. Here is my issue: Type GFCI Outlet- Eaton TR Installed mid to...
Replies
2
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock