Discuss Faulty RCD, electrical board or unknown in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi

Hoping to get some insight from people, as I have had two electricians check the fault, to no avail.

The most obvious fault is the RCD is tripping.

It trips randomly. I have tried a process of elimination and it is not a faulty item.

It will trip when cooker is turned on, when washing machine is powered, when kettle is turned on, shower, nespresso machine. All are on separate MCB's.

It is not tripping for certain items, tvs, sky box, fridge, outdoor lights.

Although the RCD is tripping, the MCB that is linked to the item that is causing the trip, is not.

Had my cousin have a look, who is an electrician for 20 years. Deduced (and hoped) it must be a faulty RCD, as everything visually seemed fine and went through wiring at the box. However he had limited tools with him and no RCD to replace.

I called another electrician I know, who had a spare RCD handy. Replaced, however the new RCD tripped. Went through the above with him and was unsure what the cause is. It was late last night so sent him away and is returning today.

Could people perhaps give some ideas, for me to throw at him.

He did try his multimeter on RCD/MCB, this caused the RCD to trip again.

I had a read through some threads, some mention earth leakage?

Thanks
Michael
 
Classic symptoms of a N to E short (fault)

this could be on any circuit, not necessarily fed from the RCD.

common locations for this type of fault are
oven, grill, hob.
outside lights
garden lighting
any new pictures or shelves etc. Been put up?
 
Classic symptoms of a N to E short (fault)

this could be on any circuit, not necessarily fed from the RCD.

common locations for this type of fault are
oven, grill, hob.
outside lights
garden lighting
any new pictures or shelves etc. Been put up?
Any reasons why this would happen suddenly?

No, nothing new in terms of pictures, etc
 
It will become apparent when the spark finds the fault.
water ingress, physical damage, rust or wear and tare are often the cause.
 
If you have an RCD tripping and the actions that trigger it is on different circuits (you mention cooker and shower) there is a good chance it's a perpetual Neutral-Earth fault with either a single appliance/accessory or the fixed wiring.
Insulation Resistance testing is the way forwards.
Ill pass this onto the electrician. I did mention the shower/cooker but fault will still occur if the mcb's are turned off for these applicance and occurs for different items on different mcbs.
 
Ill pass this onto the electrician. I did mention the shower/cooker but fault will still occur if the mcb's are turned off for these applicance and occurs for different items on different mcbs.
That is the really difficult thing about finding Neutral to Earth faults. The MCB's only typically isolate the live, the neutrals are all joined together for the rcd protected circuits. So turning off a circuit doesn't remove the possibility that the circuit has a Neutral to Earth fault.

Here are two quite bad drawings done on my phone (I'm waiting to gain access to a site to start work!)
Two loads, the MCB for load 1 is turned on, the MCB for load 2 is turned off, no faults.

1640165359570.png

Then with a Neutral to Earth fault on Load2 which still has the MCB turned off, you'll see some of the N current from Load 1 finds a path through the fault. The RCD notices and says "some electricity has gone the wrong way" and trips in case it's path is through a person.
1640165635536.png

A decent electrician can use standard test equipment to identify the presence of the fault and diagnose further from there.
(EDIT both MCBs are supposed to be joined with a red line at the bottom)
 
Last edited:
That is the really difficult thing about finding Neutral to Earth faults. The MCB's only typically isolate the live, the neutrals are all joined together for the rcd protected circuits. So turning off a circuit doesn't remove the possibility that the circuit has a Neutral to Earth fault.

Here are two quite bad drawings done on my phone (I'm waiting to gain access to a site to start work!)
Two loads, the MCB for load 1 is turned on, the MCB for load 2 is turned off, no faults.

View attachment 93300
Then with a Neutral to Earth fault on Load2 which still has the MCB turned off, you'll see some of the N current from Load 1 finds a path through the fault. The RCD notices and says "some electricity has gone the wrong way" and trips in case it's path is through a person.
View attachment 93302
A decent electrician can use standard test equipment to identify the presence of the fault and diagnose further from there.
(EDIT both MCBs are supposed to be joined with a red line at the bottom)
Thanks Tim, presume he'll find the fault today.
 

Reply to Faulty RCD, electrical board or unknown in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
619
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock