First house, want to retrofit Underfloor Heating. Many Questions

Discuss First house, want to retrofit Underfloor Heating. Many Questions in the UK Electrical Forum area at ElectriciansForums.net

O

OnlyHumanHere

Hi there,


So first things first, just bought myself my first house 20151120_154608.jpg. 1920's build in Wiltshire. Should have the keys to it next week, can't wait.


Floor plan l8u81i4uNEiqib8Bo7vlxA.jpg




First problem is, no gas mains in the village. This means it currently has an immersion heater to supply hot water 20151125_165423.jpg20151125_165447.jpg, storage heaters for heat and the oven/hob connected to gas bottles stored outside on the side of the house.


So, after doing a bit of research and planning with my wife, we want to scrap the storage heaters 20151120_161302.jpg 20151120_161337.jpgand go for water UFH with a free floating 8mm laminate flooring Something on the lines of this . Looking around, I think prowarm seem to do a good job with supplying all the parts we need, being bought from Theunderfloorheatingstore (regarded fairly highly online and seemed very helpful on the phone).


Now, my main concern is what to do with the heating element. I've spoken to a few specialists and I've been told either keep the immersion heater for the sink/bath water and get something like a 'Slim Jim'ehc-slim-jim-electric-flow-boiler-26463-p.jpg electric boiler for the UFH. Obviously the guy that recommended that was the website that sells it. However, again it's reviewed rather well and it'd be nice to keep all the product coming from one place.


Another plumber I spoke to recommended to scrap the immersion heater and get a combi boiler. He did say that if it was him, he would probably look at LPG combi boilers over an electric boiler for the long term cost saving (did a bit of research and yes, lpg is much cheaper than electric). However, when it comes to boilers, I'm completely lost as to what I need.


So my questions are...


* Keep the immersion tank or scrap it?
* Get an LPG combi boiler, electric combi boiler or just a stand along boiler for the UFH and keep the immersion tank.
* If I was to take the immersion tank out, should I put the new boiler in it's place? If so, would I need 1 or 2 UFH manifolds for each floor?
* I was thinking about putting the whole system (manifold and boiler) under the stairs20151120_161232.jpg, would that make sense?
* Apart from the kitchen (which is tiled) and the reception (which is original parquet), the rest of the house is carpeted, is it relatively straight forward to just rip the carpet up, lay down the floating floor, insert piping, cover and just throw the laminate on top?
* One guy I spoke to said I would probably need to manifolds, 1 for each floor. Is that right?
* rippiing up the Parquet20151120_161343.jpg and tiles in the kitchen, is there anything I should know before doing so?


I plan to try and get most the humping and dumping, laying the insulation for the piping, the piping and laminating myself, however I will be getting professional help for the installation and testing of the equipment.




Final Question, with multizone UFH...is the NEST thermostat (Gen 2) still a good option?






I hope I haven't made things too complicated.












TL: DR....Want to install UFH, in the UK, what is a recommended brand? Should I scrap my Immersion heater for an electric or LPG combi heater? Is it all worth it?
 
I'd go for a gas combi boiler over the electric option.
Boiler location will depend on where the flue, discharge, condensate and gas supply can be sensibly located. There are rules about clear access required in front of the boiler.
As far as insulation goes the more of the floor you can dig out and fill with insulation the better, but you'll need to get professional help to know what can or can't be done without affecting damp proofing etc etc
 
Welcome to the forum.
I approved your post for general forum although you maybe given access to the DIY section and thread relocated when admin is next on line unless you can tell us your Electrical background and qualifications.

Please note when installing underfloor heating, it will require a series of tests at different stages of the install, not doing this with make the warranty invalid to the company you sourced it from and also to the Electrician who connects and signs it off.
 
Welcome to the forum.
I approved your post for general forum although you maybe given access to the DIY section and thread relocated when admin is next on line unless you can tell us your Electrical background and qualifications.

Please note when installing underfloor heating, it will require a series of tests at different stages of the install, not doing this with make the warranty invalid to the company you sourced it from and also to the Electrician who connects and signs it off.


Ye, I'm aware it all needs to be certified. I plan to get most of the stuff in position and fitted, then get someone in the local area to wire it all up and test it all. Multizoned UFH requires a of wiring from thermostats to actuators on the manifold etc...well beyond my expertise.
 
I'd go for a gas combi boiler over the electric option.
Boiler location will depend on where the flue, discharge, condensate and gas supply can be sensibly located. There are rules about clear access required in front of the boiler.
As far as insulation goes the more of the floor you can dig out and fill with insulation the better, but you'll need to get professional help to know what can or can't be done without affecting damp proofing etc etc

There's no mains gas in the village :( So that's out of the question unfortunately. That's why it's a ---- up between 'maybe' LPG combi or Electric combi.

I was looking at this stuff as the insulation below the piping it's nice and thick.

My main concern is the upstairs. until i have the keys, i have no idea what is under the carpet, it's a loft conversion as the building used to be a single floor school, I'm guessing it's just joists, which will probably throw a spanner in the works with regards to keeping things simple.
 
Welcome to the forum.
I approved your post for general forum although you maybe given access to the DIY section and thread relocated when admin is next on line unless you can tell us your Electrical background and qualifications.

Please note when installing underfloor heating, it will require a series of tests at different stages of the install, not doing this with make the warranty invalid to the company you sourced it from and also to the Electrician who connects and signs it off.

I've never yet seen plumbers test underfloor heating other than filling it up and seeing where the water ****es out. What tests are you thinking of
 
Im with dave, put in a LPG combi boiler the position has varying factors as you cant vent onto a neighbouring property. I would scrap actuators and just use a zone valve for a simple setup. Keep the immersion just as a safety net really and fit a valve to divert the water from the combi to the immersion, or fit a system boiler.
 
There's no mains gas in the village :( So that's out of the question unfortunately. That's why it's a ---- up between 'maybe' LPG combi or Electric combi.

I was looking at this stuff as the insulation below the piping it's nice and thick.

My main concern is the upstairs. until i have the keys, i have no idea what is under the carpet, it's a loft conversion as the building used to be a single floor school, I'm guessing it's just joists, which will probably throw a spanner in the works with regards to keeping things simple.

If your comment about lpg was in response to me then all I can say is that LPG is gas!

Under the carpet will be wooden floor on joists. You can buy products designed for installing underfloor in such situations, but as ever you need to put lots of insulation in there

Those panels you've linked to are the kind of thing but you'll need a good depth of insulation under them!
 
Last edited:
Im with dave, put in a LPG combi boiler the position has varying factors as you cant vent onto a neighbouring property. I would scrap actuators and just use a zone valve for a simple setup. Keep the immersion just as a safety net really and fit a valve to divert the water from the combi to the immersion, or fit a system boiler.

How on earth would they keep an immersion with a combi?
 
If your comment about lpg was in response to me then all I can say is that LPG is gas!

Under the carpet will be wooden floor on joists. You can buy products designed for installing underfloor in such situations, but as ever you need to put lots of insulation in there

Those panels you've linked to are the kind of thing but you'll need a good depth of insulation under them!

Got ya, apologies for the confusion.

Yea, I've seen the joist solution, looks relatively straightforward (famous last words).
 
you could pipe a separate diverter/ 2port valve from the standard system to the immersion, it would have to be manually done. Bit heath robinson but could get you out a jam.

Do you mean install a diverted in the DHW pipework from the combi and the outlet pipe of the cylinder? That's going to bring a whole host of issues for compliance with water regs I think!
 
I've looked into that option but the problem is, from what I've been told, it's far more expensive to keep the house warm. My wife works at home and we have a 5 month old.
our government is keen to erect these eyesore windmills al over the land and seascape. see if they'll stick a couple up in your back garden. free leccy for your heating.
 
our government is keen to erect these eyesore windmills al over the land and seascape. see if they'll stick a couple up in your back garden. free leccy for your heating.


I personally don't mind them, thankfully though, we don't have a garden...annoyingly, we're in a preservation area and have been told we're not allowed to install solar panels on our South facing roof....madness.
 
With tin hat. OP I would suggest you contact one of the various companies that offer wet UFH systems and ask their advice and see what could be achieved. UFH function slightly differently to wall hung heating systems, at a lower constant heat. You will need adequate insulation installed for it to be economical. Digging up concrete floors, to allow for insulation/pipe & screed will not be cheap, and certainly disruptive. It might be attractive as a more modern alternative, but perhaps wall hung might be more reasonably priced. But it's your money.
 
Heating water using an electric boiler for UFH makes no sense to me, might as well use electric underfloor heating, however I am with the majority here and use LPG with a decent sized tank from Flogas or Calor, you could also use a oil fired boiler and have a tank outside if you have the space. You could either go combi or system boiler and retain a cylinder but if you do, go for an unvented cylinder they are miles better and don't require a header tank in the loft. If you go wet UFH, then I would have one manifold for living rooms downstairs and one manifold for bedrooms and a separate manifold for bathrooms. There are loads of options here depending on budget, how long you intend to stay there and how much disruption you can cope with. Get a couple of heating firms in and get them to recommend a solution / options. I am sure they will be OK with you doing some grunt work...
 
Heating water using an electric boiler for UFH makes no sense to me, might as well use electric underfloor heating, however I am with the majority here and use LPG with a decent sized tank from Flogas or Calor, you could also use a oil fired boiler and have a tank outside if you have the space. You could either go combi or system boiler and retain a cylinder but if you do, go for an unvented cylinder they are miles better and don't require a header tank in the loft. If you go wet UFH, then I would have one manifold for living rooms downstairs and one manifold for bedrooms and a separate manifold for bathrooms. There are loads of options here depending on budget, how long you intend to stay there and how much disruption you can cope with. Get a couple of heating firms in and get them to recommend a solution / options. I am sure they will be OK with you doing some grunt work...


We're in no rush to move in to be honest...I'm planning to move in after about 2 months...which is the reason why I'm happy to try my best with a lot of the work....I have time for mistakes and also don't need to worry about living in a workshop.


Is there a reason why you recommend a cylinder? Isn't just a combi on it's own with a heat on demand system better? (remember I've no idea what I'm talking about so if that didn't make sense please tell me....it kind of made sense to me though haha).

We plan to make this our forever home...it's not going to be an investment we plan to sell after doing up so we're happy to throw money in it if it makes our lives more comfortable for longer.

Unvented cylinders can last 30 years? am i right?

Don't have space outside for an oil tank...kind of just have space for gas bottles (like 100cm in height).

Our kitch oven/hop is connected to gas bottles outside but I'm not sure what kind of gas it is.

I'd say our budget...including boiler, ufh, laminate flooring is about ÂŁ10k...give or take a bit.
 
Last edited by a moderator:
2months isn't long enough to do the job properly, you're talking about removing all of the floors, insulating and relating them!
If you're going to insulate properly then you'll be putting a good 6/8" of decent insulation down, not just those daft 1" thick panels.
 
We're in no rush to move in to be honest...I'm planning to move in after about 2 months...

I'd say our budget...including boiler, ufh, laminate flooring is about ÂŁ10k...give or take a bit.
Best allow about 2k as well for some dynamite to excavate the existing floors. Seriously get some professional advice about feasibility before getting too excited about wet ufh.
 
2months isn't long enough to do the job properly, you're talking about removing all of the floors, insulating and relating them!
If you're going to insulate properly then you'll be putting a good 6/8" of decent insulation down, not just those daft 1" thick panels.


wait what? 2 months? you've got to be kidding!

How long does it take to rip carpet up and lay down some insulation? It's floating UFH, no requirement for screed. there's surely no need for the best part of a foot of insulation.
 
wait what? 2 months? you've got to be kidding!

How long does it take to rip carpet up and lay down some insulation? It's floating UFH, no requirement for screed. there's surely no need for the best part of a foot of insulation.

Sorry, I thought you'd said you wanted to do the job properly as its a house you intend to live in for a long time?
6" is half a foot, not the best part of it.
Laying ufh on top of a 1920's solid floor construction is going to waste the vast majority of the heat energy in warming up the mass of solid floor under it. If it's a hollow wooden floor construction then it hasn't got a hope in hells chance of heating anything without a lot of insulation being installed under the floor!
Years ago a I worked on one where they laid ufh into an existing wooden ground floor with just a 4" layer of fibreglass between the joists. When it was all done you could just about feel a slightly warmer patch directly above each pipe and the room was freezing.

You need a good thick insulation layer of you want to actually hear the rooms, preferably with the pipes buried in a screed on top of it to create a big thermal store.
 
We're in no rush to move in to be honest...I'm planning to move in after about 2 months...which is the reason why I'm happy to try my best with a lot of the work....I have time for mistakes and also don't need to worry about living in a workshop.


Is there a reason why you recommend a cylinder? Isn't just a combi on it's own with a heat on demand system better? (remember I've no idea what I'm talking about so if that didn't make sense please tell me....it kind of made sense to me though haha).

We plan to make this our forever home...it's not going to be an investment we plan to sell after doing up so we're happy to throw money in it if it makes our lives more comfortable for longer.

Unvented cylinders can last 30 years? am i right?

Don't have space outside for an oil tank...kind of just have space for gas bottles (like 100cm in height).

Our kitch oven/hop is connected to gas bottles outside but I'm not sure what kind of gas it is.

I'd say our budget...including boiler, ufh, laminate flooring is about ÂŁ10k...give or take a bit.

Combi's are great for small houses and few occupants (preferably men, lol) A combi has to heat water instantaneously and as the water demand grows, i.e. if there are two demands for hot water, shower and say washing up, flow will be reduced to keep the temp up. If you say start a family and have all girls (like me) then a large tank unvented of course is a god send, the boiler runs in whisper mode to heat up the tank rather than full turbo mode and as such, such is the laws of physics, it works out cheaper and better. I have two tanks, one for me and one for the girls so I don't have to negotiate who has a bath / shower when etc etc.

As for gas bottles...... mmmmm, worth a chat to flogas just to see if a proper tank is feasible, there are certain minimum distances and the like but it may be doable, who knows.
 

Reply to First house, want to retrofit Underfloor Heating. Many Questions in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock