I come across a lot of swa nowadays with no bango or earthing nut on the armour

are the new breed no longer bothering earthing the armour

I'm surprised that something like that would have got passed initial verification on something only two years old. I thought that was a pretty big requirement for swa that goes out and underground (ie for the armour to have continuity back to the MET).
 
Thanks

Any particular reason why the fly lead csa would have to be so large? The csa of the line conductors to the supply of the junction box is 2.5mm, and then the swa from that is 1.5mm.

I was going to use 2.5mm for the fly.
you're right. it's just that i always have 6mm Gn/Y on the van but not always 2.5.
 
Is it not earthed at the other end of cable?

Not as far as I can see. This is the other end:

20210625-172453.jpg


So there is nothing linking the armour OR the metal clad switch box to the cpc...
 
SWA is only required to have the armour connected at one end (if the armour is not being used as a CPC), as already mentioned, so it may well comply.
However, I always connect the armour at both ends and at every joint, where applicable, just to be sure. I believe most sparks would do the same.
 
SWA is only required to have the armour connected at one end (if the armour is not being used as a CPC), as already mentioned, so it may well comply.
However, I always connect the armour at both ends and at every joint, where applicable, just to be sure. I believe most sparks would do the same.
If it is going to be earthed at one end I would always say it must be the supply end, lower Zs on the armour and less risk of something stupid being done at the load/accessory end.

Like the above example! If the armour is earthed, it is fortuitous by means of the back box and not by any acceptable connection.

To add: I would agree that it should be earthed at both ends if practical, exception usually is a feed to a TT'd building/caravan where the cable is TN and the end is a plastic gland as you are using only L & N and putting in a local rod for the RCD/onwards installation.
 
Last edited:
I think what your 1st home exercise has shown is a Golden Rule you should apply on jobs - test and inspect first before you make any changes.

It might well be the installation broken/unsafe to begin with, and that is a whole extra set of donkey balls to suck when you go to test your own work and find something amiss.
 
I tend to only earth (bango) the supply end , just how I do it…

sometimes I banjo both ends but only when the wind is blowing east
 
Yeh, it is a bit poor isnt it. I thought my criticism may have been unjustified as i thought both ends had to be connected to the cpc. However, then i check the termination at the other end and A. it isnt connected there either and B. the metal back box isnt connected either.


I think what your 1st home exercise has shown is a Golden Rule you should apply on jobs - test and inspect first before you make any changes.

It might well be the installation broken/unsafe to begin with, and that is a whole extra set of donkey balls to suck when you go to test your own work and find something amiss.

You are absolutely right. I shouldn't have assumed that just because it was almost brand new/done a few years ago by a big firm that it was done correctly.

I am glad i took the time to inspect it/ask these questions first.
 

Reply to First little job on own house - advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
856
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
281
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
419
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock