Hi all, I have a few questions regarding a TT system. First time ive worked on one (Self employed now and throughout my apprenticeship and self employed career I haven't had one before) 16mm2 Tails coming in from the rec. There is 2x 2.5 (looks about right) Single earths going to the incoming gas and one disappears towards water boards stop cock in the pavement. The property has a 30mA RCD main switch. I'm right in thinking I need to upgrade tails to 25mm2 and bonding to 10mm2. I will install a Earth Stake with 16mm2 earth to the fuseboard. Does the RCD man switch need to be changed to a lower mA? Is there a maximum length that the earth stake can go? Is it acceptable to take 16mm2 from stake to the DB then take bonding from there or do they have to come from the stake? or can I put a MET in for them?

Any advice appreciated. Thanks a lot.
 
If the main fuse is <100A then 16mm² tails should be OK, main bonding should be 10mm².
30mA main switch is a bit low but does cover any circuits needing 30mA protection, it also does not provide segregation of circuits to avoid nuisance. The main earthing conductor can be calculated from the adiabatic equation, with reference to table 54.1 if applicable, absolute minimum is 2.5mm²and is unlikely to need to be 16mm². Is this a new system as surely there is already an earth electrode in place?
Put an MET in.
 
House is s very old house (before 1960's) so not a new installation. No Earth stake in place but I notice 2doors down has had 16mm Main Earth and a new Earth stake installed. I did think about asking the homeowner how long ago she had the work completed. I don't know what the main fuse is yet, but its an old porcelain fuse holder presumably containing asbestos - maybe 60A normally? What would you recommend mA for a TT system? The whole property doesn't looks brilliant, No CPC on lights, DB added to the rear to feed the kitchen and an SWA incorrectly made off in it to feed 3x sheds miles away at the top of the garden. When was there any updates in the regs regarding TT Systems? Most if not 95% of the wiring is old colours (older than 2004?) but there has been a loft conversion with lights and sockets in new harmonised colours yet no cert available? Also the new owner ( How I got the work) only got keys last Friday and paid for 2x £7-800 surveys but they didn't flag the wiring up? I presume I'm right in saying that its not right having no earth stake and only 2.5mm2 to gas and water? Bear in mind the water isn't bonded at the stop cock consumer side... its bonded in the pavement on the supplier side?
 
House is s very old house (before 1960's) so not a new installation. No Earth stake in place but I notice 2doors down has had 16mm Main Earth and a new Earth stake installed. I did think about asking the homeowner how long ago she had the work completed. I don't know what the main fuse is yet, but its an old porcelain fuse holder presumably containing asbestos - maybe 60A normally? What would you recommend mA for a TT system? The whole property doesn't looks brilliant, No CPC on lights, DB added to the rear to feed the kitchen and an SWA incorrectly made off in it to feed 3x sheds miles away at the top of the garden. When was there any updates in the regs regarding TT Systems? Most if not 95% of the wiring is old colours (older than 2004?) but there has been a loft conversion with lights and sockets in new harmonised colours yet no cert available? Also the new owner ( How I got the work) only got keys last Friday and paid for 2x £7-800 surveys but they didn't flag the wiring up? I presume I'm right in saying that its not right having no earth stake and only 2.5mm2 to gas and water? Bear in mind the water isn't bonded at the stop cock consumer side... its bonded in the pavement on the supplier side?

I have never installed a 'new' TT system, but have worked on several existing ones. If you have a copy of the latest yellow OSG, it gives a couple of suggestions for a new TT CU installation. Somewhere you will have an 'earth stake', either a rod or more probably an old metal pipe. Have you consider asking the DNO for conversion to PME, if the customer is willing to pay? The way that you have described the main fuse, I would be getting them to have a butchers anyway. If you do install a new earth stake, you may wish to ask members advise on sitting, and may consider testing first (if your MFT provides facility), or it may prove expensive in terms of numbers of stakes!

Think most sparks run a 10mm cable to a stake, only because that's what they have in the back of the van, but Richards way is the correct way to calculate the size of earthing conductor.

Reg 544.1.1 specifies the size of main protective bonding conductors, 544.1.2 details where services should be bonded.

Sounds like some of the property is due a rewire, certainly the circuits with no cpc. What did your survey of the property suggest?
 
good point. richard. i think a more thorough investigation is required. maybe see if he can get a Ze for the installation.
 
If the "bonding" to the water goes to the suppliers side then this is probably the main earthing for the property; using the metal water pipe as the main earth, which is no longer allowed.
 
but what sort of a Ra would you get when you rodded a smart arse?
 
Are you sure that the cable that disappears into the pavement is not to an earth stake.
The water would be bonded inside the property , not outside.

Aye that could be possible. They are nearly all unused now round here, but it is very common to see the old earth stake hugging the front brickwork of the house with it's unsheathed earth wrapped round it.

I'd be tapping in a temp earth stake and getting the DNO to quote for a PME if available. Always the best option in my book.
 

Reply to First time working on a TT Sytem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have added a consumer unit and an earth stake to this so called temporary supply. This is a full rcbo board apart from the mcb to the spd...
Replies
11
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
906
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock