- Reaction score
- 1,698
Thanks for all the info. It doesn't get any clearer!Good morning everyone. As mike suggested I disconnected the SL at fan - no change.
I have fitted a different timer - no change.
Cables are not particularly close or bunched - so I think unlikely it's inductive from an adjacent cable.
Showing between 7v - 11v between L/N at one of the LEDs.
I have wired a pendant with 100w lamp across one of the LEDs L/N and problem gone, but obviously I can't keep that there!
I'm using .47uf 100r capacitor as snubber, but are these large enough (or whatever), as the 100w lamp appears to be able to dissipate the stray voltage.
Yet again I appreciate all the help.
Have you tried disconnecting S/L from the timer and measuring the voltage on the 'Manrose' S/L terminal (if any).
I'm presuming all the lamps (by which I mean the bulbs themselves) on this circuit are mains voltage, there's no led driver or electronic transformer on this circuit, no shaver socket or charger, or anything we're missing?
Last edited: