Discuss Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

I don't remember a 12v driver/transformer in any of the other sketch's, is it supplying 12v to just that one bulb or all of them?
See post #33. Supplying just that bulb is my understanding. It was rather hidden amongst all the dialogue and explains why the halogen is not itself an adequate 'snubber'.
So I took the liberty of adding it to the diagram!!
 
As soon as I disconnect the timer SL the flickering stops.
I am still fascinated by this from post #21.
I feel it is significant, and if it still holds true gives a 'fix' I described previously.
Might be interesting to see if there's any uA or mA ac (or dc for that matter) flowing at that SL terminal when lights are off?
 
I suspect that the electronic circuit in the manrose 1351 timer is acting as a dc voltage source circa 14V at its SL output. Tomorrow I will draw you a sketch of what I think the innards of the 1351 looks like. This small voltage current source is sufficient to light the low wattage LEDs dimly. Being dc the snubbers are ineffective since they are a series capacitor -resistor combo.

What we need is a voltage dependent way of isolating the SL output on the 1351 from the conductor going back to the SL on the connector strip to which the LEDs are connected. A zener diode is a possible way. Please would you obtain a few - say 5 to 10 - of these 24V Zener diodes. Here is a link to Rapid Electronics website but using the Amazon and search for 'BZX85C24' you will probably find some of them:

Vishay BZX85C24 24V 1.3W Zener Diode - https://www.rapidonline.com/vishay-bzx85c24-24v-1-3w-zener-diode-47-3088

When you have them you will use another connector strip to mount either one or two of these Zener diodes in series with the SL just as it connects to the SL terminal on the Manrose 1351 timer. I will show you how in a picture once you have the Zener diodes. The diodes need to be connected the right way round. For voltages less than 24 V they do not conduct but over 24V they become conducting. Thus they act like voltage controlled switches. Using one puts a block on V < 24V whereas two in series would block when V < 48V. Thus for V of 14V at SL on the 1351 the circuit path back to the LEDs is effectively open circuit so no current flows to illuminate the LEDs dimly. Well this is my analysis but the proof is by testing the scheme out.

Note well: Just because they are 25 V Zeners their leads are at mains voltage so they will need insulating and an enclosure.

See my sketch attached.
 

Attachments

  • IMG_1599.jpeg
    244.7 KB · Views: 9
Last edited:
I suspect that the electronic circuit in the manrose 1351 timer is acting as a dc voltage source circa 14V at its SL output. Tomorrow I will draw you a sketch of what I think the innards of the 1351 looks like. This small voltage current source is sufficient to light the low wattage LEDs dimly. Being dc the snubbers are ineffective since they are a series capcitor -resistor combo.

What we need is a voltage dependent way of isolating the SL output on the 1351 from the conductor going back to the SL on the connector strip to which the LEDs are connected. A zener diode is a possible way. Please would you obtain a few - say 5 to 10 - of these 24V Zener diodes. Here is a link to Rapid Electronics website but using the Amazon and search for 'BZX85C24' you will probably find some of them:

Vishay BZX85C24 24V 1.3W Zener Diode - https://www.rapidonline.com/vishay-bzx85c24-24v-1-3w-zener-diode-47-3088

When you have them you will another connector strip to mount either one or two of these Zener diodes in series with the SL just as it connectes to the SL terminal on the Manrose 1351 timer. I will show you how in a picture once you have the Zener diodes.

Note well: Just because they are 25 V Zeners their leads are at mains voltage so they will need insulating and and enclosure.

See my sketch attached.

Nice thinking. It will be interesting to see where this goes. Seems like it is definitely linked to the fan somehow.
 

I turned up this ‘open up’ of a manrose timer fan. If you look at 4m50s you will see the chap has sketched the timer circuit and shows how the SL input is connected to the circuit. Just by looking at the adjacent circuitry of diodes and r3istors and capacitors you can see the possibility of dc current flowing out of the SL terminal. Also the measured 14.1V at SL wrt to N is in accord with the Zener diode voltage rating of 14.7V. The SL input responds to the light switch closure during the negative half cycle of the mains voltage sinusoid.
An external Zener may work then if connected in the way I showed earlier. May need to trial a few blocking voltage levels though.
 
Nice thinking. It will be interesting to see where this goes. Seems like it is definitely linked to the fan somehow.
I think that's the problem, the OP's fan has its own timer originally he had both the Manrose unit and the timer on the fan operating, did advise him to disconnect the fan timer, but it may need to be by passed.
 

I turned up this ‘open up’ of a manrose timer fan.
Thank you so much Marconi for that.
Just a heads up that the OP has a separate run-on timer, which I think is the one below.
I believe he has connected the fan SL and L together at the fan, and then connected that combination to the Manrose 1351 unit. So I think what we are battling with is the SL of the Manrose 1351, which may or may not be a similar thing?
https://www.NoLinkingToThis/p/manrose-1351-remote-bathroom-fan-timer-control/83794?

I haven't yet found a circuit diagram for the 1351, only the usual installation bumf that is everywhere.
 
Last edited:
Hi Clanky
If you haven't given up already (and by the 70th post perfectly understandable) could you take a pic of the insides of the Manrose 1351 timer and post it here. I believe you bought a second one in case the first was faulty (which it wasn't)?
PS from the pic below, it may be slightly tricky to get into it - don't break anything, I'd rather you left it!

IMG_0239.jpeg
 
Last edited:

Reply to Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
700
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
635
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
321

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock