Discuss Flickering LED lights in the UK Electrical Forum area at ElectriciansForums.net

Baz1974

DIY
Reaction score
1
Sure this has been answered before, can’t find a specific answer though.
My house was rewired in 2021 and as part of the rewire I had LED lights put in every room, so 70-80 in total. Now about 12 months after the rewire one of the lights in one room (4 LEDs in the room, not on a dimmer) comes on dimly then every 60 seconds or so will go to full brightness, then back to more dimmer. After about 5 minutes it will stay on full brightness.
I checked the connections and seemed fine so I switched it with another unit in the house, the same problems continue with the first unit while the one I switched too worked perfectly……for about two weeks…….then it’s doing the same issue as the first one. Any solution as I don’t think it’s the unit and the wiring seems ok. I’ve attached pictures of the light and the connecting box.
IMG_4918.jpegIMG_4917.jpegIMG_4916.jpeg
 
My guess is that it's at the end of a chain and the fault is at the other end of the cable that feeds it - check the terminations of all four!
 
Hang on - are you now saying that you started with one faulty location and now have two?
 
Hang on - are you now saying that you started with one faulty location and now have two?
The original unit still has the same fault despite moving it to another room. Is it possible that being left flickering for 12 months has “nobbled” the light? They’re a bit more of a complicated unit that the electrician who did the rewire talked me into getting. They have three light settings built into the unit, white, warm and daylight. More components = potential for more faults?
 
The original unit still has the same fault despite moving it to another room. Is it possible that being left flickering for 12 months has “nobbled” the light? They’re a bit more of a complicated unit that the electrician who did the rewire talked me into getting. They have three light settings built into the unit, white, warm and daylight. More components = potential for more faults?
I'd say it's not impossible. If you've the competency to do so, remove it completely and put a cable and 13a plug on it, see what it does on the bench. Warranty replacement beckons!
 

Reply to Flickering LED lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
682
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
197
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Done a job yesterday, remove old 12v halogens and replace with mains, gu10 downlights. Fitted some LED gu10's no issues. Got a call today saying...
Replies
9
Views
850
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock