NDG Elecs

-
Esteemed
Arms
Reaction score
1,751
Hi One and All.

Fault finding today. Narrowed it down to one leg of RFC between N&CPC.

What puzzled me was the fluctuation in the IR test. Normally I find the reading stabilises after a short period (5-20 seconds). Today the reading was constantly jumping between 20Mohms with an occasional flicker towards 0.00Mohms. The readings were up and down like a yo-yo with this intermittent jump to 0.00 every 10 seconds or so. If Lee Evans (manic comic from +15yrs ago) was an IR test result then this was it!!

I realise digital meters have their foibles and an anologue meter may have told a different story, but I am intrigued to discover any views or thoughts or knowledge on the above.

On this particular installation there are three points affected, all fed individually by a single T&E, so there is at least one hidden junction somewhere, possibly more. But that's an aside really.

Thanks!

Neil
 
I might initially worry about your test meter and leads, but if this variation was only found on this circuit then I would be expecting some vibration at the point of failure allowing the fault to escalate at times or volatile conductive contamination that is flowing, evaporating or jumping from the applied voltage.
Possibly there is a failing capacitor that breaks down when fully charged.
Odd one certainly.
 
I've had very similar readings before on faults, usually it has turned out to be a charred burnt section of cable due to mechanical damage, or charred terminations, both caused by long periods of arcing. Sometimes you can break it down into a 'proper' reading by zapping it with 1000v. Just be certain the affected part of the circuit is completely isolated from anything sensitive.
 
Agree what the others have said but i would also be looking at the possibility of water getting into something.After the water has broken down the insulation then the arcing starts across the charred part.Are there any outdoor lights or sockets on the faulty circuit?
 
Just remembered what I forgot to put in the OP also; at 250V the reading stabilised and was clear (300Mohms ish). At 1000V the reading was like at 500V.

Thanks for replies so far. Pushed for time at minute but will respond later.
 
Either a flashover between two bits of stuff (e.g. mangled conductors) very close but not quite touching, a capacitor likewise (maybe part of a delta suppressor cap in an appliance still connected) or perhaps some oddball like an earth-present indicating neon lamp in an extension (nasty things). There are possible failure modes of electronic appliances that might cause this but as you've presumably unplugged most or all, that is stretching the bounds of probability.
 

Reply to Fluctuating IR reading. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
732
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
4K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock