Just started PAT testing and trying to understand why stuff fails. Recently had a large fridge fail. The cable was scuffed with a slice of the flex missing so the yellow wire was visible but not the copper. The readings on the tester were 0.6 plus in various places. Could it just mean the cpc is damaged so a mew cable is all that’s needed or could there be something else going on. Out of interest I did other tests which it passed.

Obviously I did fail it and removed the fuse and told the Damsel to call an Engineer but wanting to learn the whys...
 
Just started PAT testing and trying to understand why stuff fails. Recently had a large fridge fail. The cable was scuffed with a slice of the flex missing so the yellow wire was visible but not the copper. The readings on the tester were 0.6 plus in various places. Could it just mean the cpc is damaged so a mew cable is all that’s needed or could there be something else going on. Out of interest I did other tests which it passed.

Obviously I did fail it and removed the fuse and told the Damsel to call an Engineer but wanting to learn the whys...

What particular test failed, and what units is the 0.6 figure in?
 
Could it just mean the cpc is damaged so a mew cable is all that’s needed
More than likely. Also worth checking earth connection in plug (as usual).
Out of interest I did other tests which it passed.
The IR test joins L and N together and tests between them both and cpc.
If cpc is questionable then this test doesn't really mean a lot, and will need doing again once cpc is functional. For example if cpc was completely cleanly broken this test would still pass.
 
More than likely. Also worth checking earth connection in plug (as usual).
I've had fails due to corrosion on the earth plug. A good clean with a scourer type pad soon had things passing again. This has mainly been on 110v commando plugs but I have seen it on BS1363 plugs that have lived a harsh life.
 
I've had fails due to corrosion on the earth plug. A good clean with a scourer type pad soon had things passing again. This has mainly been on 110v commando plugs but I have seen it on BS1363 plugs that have lived a harsh life.
That post of mine should have said 'earth PIN' and not 'earth plug' ?
 

Reply to Fridge Fails Class 1 Test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
HI guys, new to PAT testing and here. I recently completed an online course in order to carry out PAT tests annually in 10 rented houses...
Replies
45
Views
7K
Hi Guys Long time since I last posted but I have a problem I'm stuck on. My company uses a few industrial hand held glue guns. We have been...
Replies
10
Views
2K
When I bought my house we had it inspected before buying to highlight faults, so the inspection and testing done by RICS Chartered Surveyor and...
Replies
13
Views
3K
Hello, I am a Trainee here on the Forum. I am seeking some further advice/input on a specific technical matter of importance to me. Briefly, I...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock