Doing an EICR in a property and on arrival found that the fuseboard and supply,cutout and main fuse are all in a converted shower room which used to be a large cupboard.

The board is enclosed in a small wooden boxed in effort.It is 1.4m from the edge of the shower tray so technicallty outside zones specified in on site guide.

Just a quick question........what would you do in this situation?
 
It's a nuisance when an mcb trips at the best of times, so much worse when you're half way through a shower.
Now with this revolutionary idea there's no need to faff about wet and naked, looking for your dressing gown in the dark before traipsing through the house to the board.
Just reach out and reset it immediately. Brilliant.
 
As above, I think 'common sense' is more the issue than the regulations. I expect the regulations could be manipulated either way to say that a CU in a shower is acceptable or not. I was asked recently if I would relocate a CU into a bathroom, I declined and offered a better suggestion that was accepted.

As for coding, I personally would find that a bit difficult, perhaps a C3 or no code, perhaps a C2 (If there was any chance of the CU being hit with water from the shower). A picture would be good?

What thoughts did you have (to the OP) on what code it should be?
 
Last edited:
It's a nuisance when an mcb trips at the best of times, so much worse when you're half way through a shower.
Now with this revolutionary idea there's no need to faff about wet and naked, looking for your dressing gown in the dark before traipsing through the house to the board.
Just reach out and reset it immediately. Brilliant.

Haha. I like this one...
 
As it is outside of the zones, it does not appear to be immediate danger. However, is the board likely to be exposed to water jets from the shower? If it is likely, perhaps a C2. If it is not likely use a C3 with a view to changing the wooden enclosure to something more suitable such as this:

Meterboxes Direct Online Shop | Enclosures / Sealed Boxes | Weatherproof electrical cabinet -IP65 rated(600x400x230mm)
That's going to look lovely in the customers shower room eh? And how is he going to get the cut-out in it?
 
Last edited:

Reply to Fuseboard in shower room in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone had encounters with rogue landlords? I will tell my short story (and keep it as short as possible) I had a call a few weeks back from...
Replies
70
Views
7K
Doing an EICR today and customer has a tumble dryer in the shower room. Room is an L shape with shower directly in front of door and around...
Replies
10
Views
9K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
Was hoping someone could offer some advice as I cant access my Regs book at the moment( bloody online digital version.....don't recommend this to...
Replies
15
Views
3K
M
What's your take on a plate switch controlling a light in an en-suite shower room? It's positioned outside the shower room on the wall by the...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock