Fitting a new CU today (domestic TT) and using "Fusebox" for the first time - 14 way Type A RCBO board, 9 ways used 5 spare.
All good until testing RCBO trip times - 7 test perfect, but 2 (both 6A) tripping during half test, 1 @ 0 the other @ 180. All loads disconnected, tested again, same results. I'm assuming these 2 are faulty or have I missed something at the end of a long day?
Ramp test for all 9 RCBOs trips @ 18mA. To my mind this is much too low, but I assume this is the design as they are all the same. (MFT recently calibrated and working fine as far as I'm aware from other tests and recent use.)
Anyone else had any issues with these RCBOs / the brand?
I have another 6 way RCBO board to fit this weekend so a little anxious...