Discuss Lights RCBO keeps tripping randomly in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps tripping with no switches or even bulbs being attached to the circuit. Even trips when other appliances that are not on that lighting circuit are not being turned on or off.

The fusebox was replaced 2 years ago with RCBOs. The wiring is old however a condition report was issued as a pass at the time the fusebox was replaced. The ground floor and upstairs lighting are on a single 6A RCBO with borrowed neutral, this has worked fine until now.

During a insulation resistance test there is a low reading on the ground floor lighting however still a pass.

The electrician and I did the following scenario/tests:
  1. Replaced lighting 6A RCBO - RCBO trips randomly within minutes or few hours
  2. No bulbs attached and no light switches pressed - RCBO trips randomly within minutes or few hours
  3. Bulbs attached no light switches pressed - RCBO trips randomly within minutes or few hours
What are thoughts on the possible root cause/issue?

Could the ground floor lighting wiring insulation have become damaged/degraded?


Thank You in advanced.
 
Dont like the sound of a borrowed neutral but if been working ok for 2 years unlikely to be that.

Are there any external fittings as with amount of rain lately, ingress of water could be a cause.

The wiring could have deteriorated but unlikely in my view unless disturbed recently.

How 'Low' a reading on insulation test? If lower than 2Mohms (1Mohm min requirement) it should have been investigated and initially categorised as 'FI' on the EICR (as should the borrowed N) and shouldn't have been signed off as Satisfactory.
 
Exactly my thoughts too:
Are there any external fittings as with amount of rain lately, ingress of water could be a cause.

How 'Low' a reading on insulation test?

Any recent DIY or lights changed?
Also consider ramp testing the RCBO, or using earth leakage tester to find out how close to tripping it is normally.
 
Outside light or security light.
full of water giving a N to E fault on that circuit.
slight changes in the N voltage cause current to flow through the N coil of the lighting rcbo and hey presto off it trips.

to test the theory, remove outgoing lives from rcbo. If it still trips randomly then we know there is a current flowing in the N cable that should not be there.

if I am right then I will send you a bill for remote fault finding and diagnostics.
if I am wrong, damn I need to get the crystal ball recalibrated.
 
DefyG said:

Are there any external fittings as with amount of rain lately, ingress of water could be a cause.
No electrical external/outdoor fittings.

DefyG said:

How 'Low' a reading on insulation test?
Sorry don't have the actual reading to share that was taken, just that electrician said it was a "low reading but still a pass”

Any recent DIY or lights changed?
No recent DIY or lights changes made
 
DefyG said:

Are there any external fittings as with amount of rain lately, ingress of water could be a cause.
No electrical external/outdoor fittings.

DefyG said:

How 'Low' a reading on insulation test?
Sorry don't have the actual reading to share that was taken, just that electrician said it was a "low reading but still a pass”

Any recent DIY or lights changed?
No recent DIY or lights changes made

It's a shame there are no IR figures available.

Was the RCD ramp tested?
 
It's a shame there are no IR figures available.

Was the RCD ramp tested?
Hi, No RCD was not ramp tested. At the time Fusebox was updated to RCBOs in 2021 the reading for both lights upstairs and lights downstairs was following test results section attached.

Thank you
 

Attachments

  • lights.png
    7.6 KB · Views: 15

Reply to Lights RCBO keeps tripping randomly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
892
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
397
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
727
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock