Hi,
I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted.
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I thought borrowed neutrals at first, but why would the 32amp ring circuit trip at the same time???
 
It could be there's an interconnection of neutrals in the property, which wouldn't have been picked up on an old board without rcd.

Was any testing done prior to board change?

Temporarily connect all 3 lighting circuits to the same rcbo, and see if it holds.

Old properties where upstairs and downstairs lights shared a switch box, it was a common fault where neutrals got mixed up.
 
Sometimes you come across an interconnection between a socket circuit and a lighting circuit. Usually on older properties, an example might be where an outdoor light was originally fed by an FCU on the ring, but later someone gave it a switched live from a nearby lightswitch.

You're going to have fun with this one, it sounds like you have 3 circuits connected to the suspect one. Testing 'by the book' doesn't usually pick these faults up.
 
It sounds like more than one issue, but you'll have to do some testing to see where the inter-connections are, and then track them down.
Be extra careful as a disconnected lighting Live wire at the CU could be energised via the sockets RCBO.

Some things to look for:
-a DIY addition where someone tried to power something from a light switch and then realised they had no Neutral, and the nearest socket was raided
-A security light that someone wanted to add a switch to
-anything a plumber has touched regarding heating controls and immersion
 
Its always a good idea to test everything when the Cu is disconnected.
To be completely fair, no one tells you at college to test for inter-connections.
It normally takes a nightmare experience to begin to appreciate the value in some interconnection tests before a shared RCD or no-RCD board change!
 
It sounds like more than one issue, but you'll have to do some testing to see where the inter-connections are, and then track them down.
Be extra careful as a disconnected lighting Live could be energised via the sockets RCBO.

Some things to look for:
-a DIY addition where someone tried to power something from a light switch and then realised they had no Neutral, and the nearest socket was raided
-A security light that someone wanted to add a switch to
-anything a plumber has touched regarding heating controls and immersion
Here's one for you Howard that i had the other day.

A 2 phase supply feeding 2 sub mains via 100ma time delayed rcds. (TT earthing)

L1 sub main feeds a bio mass boiler and an outbuilding.

L2 sub main feeds solar and a pump room.

Phase one had a L to Earth fault damaged cable touched the tin foil wall insulation.

Caused 3 rcbos to trip in various locations, 2 of them on the opposite phase.

The fault being all Upstream of these rcds/rcbos.
 
To be completely fair, no one tells you at college to test for inter-connections.
This is one aspect where the ROI (AFIK, not worked there) has a good policy or requiring testing to show that all circuits are independent.
It normally takes a nightmare experience to begin to appreciate the value in some interconnection tests before a shared RCD or no-RCD board change!
Indeed!

Being a bit paranoid after discovering a friend's house had two crossed-connected RFC, as well as lighting borrowed neutrals, I try and IR between circuits before they go back in for use.
 
Hi,
I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted.
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I thought borrowed neutrals at first, but why would the 32amp ring circuit trip at the same time???
Thanks for all the input - looks like a day of testing tomorrow.
I have tested between all the offending line and neutrals and none show any intercionnect - just to make it more interesting
 
A big fault, with lots of current flowing, causes a large dV/dt (rate of change of voltage) on the supply. That can trip RCD/RCBO by virtue of the current to earth from the cable capacitance and dV/dt.
It wasn't a big current and hardly burnt the insulation.

Bear in mind, the RA is only around 120 ohms.
 
This is one aspect where the ROI (AFIK, not worked there) has a good policy or requiring testing to show that all circuits are independent.

Indeed!

Being a bit paranoid after discovering a friend's house had two crossed-connected RFC, as well as lighting borrowed neutrals, I try and IR between circuits before they go back in for use.
Yes indeed. It's called an erroneous connections test.
 
Thanks for all the input - looks like a day of testing tomorrow.
I have tested between all the offending line and neutrals and none show any intercionnect - just to make it more interesting
From what you've described, I expect the connections between the circuits have been made via equipment, probably lighting. ie borrowed neutrals. If the circuit conductors were directly interconnected to one another, I would expect the RCBOs to be tripping with any two or more circuits connected to the CU - this is not the case.

Keep all lamps/other equipment in circuit, light switches etc in the on position, and test between circuits at 250V. Good luck
 
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I have tested between all the offending line and neutrals and none show any intercionnect - just to make it more interesting

Have you checked that each lighting circuit in turn 'mainly works' if connected on it's own, with the other circuits turned off?
It can help to take the bulbs out of stairs lighting during fault finding to remove the most likely path between circuits and verify the basics.

Complete speculation on my part but I'm wondering if you possibly have two neutrals the wrong way around, combined with a path from line on one to N on another via stairs lighting.
 
A bonded pipe touching the foil?
The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.

The location is basically a pump house wooden shed that has had insulation and ply skin.
 
Last edited:
The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.
Well that's a nice case study .... tails behind insulation in a stud wall.
It sounds like someone could have once done a bit better!
 
Well that's a nice case study .... tails behind insulation in a stud wall.
It sounds like someone could have once done a bit better!
I’ve altered it since and run both phases + N in surface mounted in some trunking.

Bit untidy looking but a bit safer
 

Attachments

  • IMG_1898.jpeg
    119.8 KB · Views: 18

Reply to RCBO tripping issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
756
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
774
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock