Hi,
I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted.
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I thought borrowed neutrals at first, but why would the 32amp ring circuit trip at the same time???
 
It could be there's an interconnection of neutrals in the property, which wouldn't have been picked up on an old board without rcd.

Was any testing done prior to board change?

Temporarily connect all 3 lighting circuits to the same rcbo, and see if it holds.

Old properties where upstairs and downstairs lights shared a switch box, it was a common fault where neutrals got mixed up.
 
Sometimes you come across an interconnection between a socket circuit and a lighting circuit. Usually on older properties, an example might be where an outdoor light was originally fed by an FCU on the ring, but later someone gave it a switched live from a nearby lightswitch.

You're going to have fun with this one, it sounds like you have 3 circuits connected to the suspect one. Testing 'by the book' doesn't usually pick these faults up.
 
It sounds like more than one issue, but you'll have to do some testing to see where the inter-connections are, and then track them down.
Be extra careful as a disconnected lighting Live wire at the CU could be energised via the sockets RCBO.

Some things to look for:
-a DIY addition where someone tried to power something from a light switch and then realised they had no Neutral, and the nearest socket was raided
-A security light that someone wanted to add a switch to
-anything a plumber has touched regarding heating controls and immersion
 
Its always a good idea to test everything when the Cu is disconnected.
To be completely fair, no one tells you at college to test for inter-connections.
It normally takes a nightmare experience to begin to appreciate the value in some interconnection tests before a shared RCD or no-RCD board change!
 
It sounds like more than one issue, but you'll have to do some testing to see where the inter-connections are, and then track them down.
Be extra careful as a disconnected lighting Live could be energised via the sockets RCBO.

Some things to look for:
-a DIY addition where someone tried to power something from a light switch and then realised they had no Neutral, and the nearest socket was raided
-A security light that someone wanted to add a switch to
-anything a plumber has touched regarding heating controls and immersion
Here's one for you Howard that i had the other day.

A 2 phase supply feeding 2 sub mains via 100ma time delayed rcds. (TT earthing)

L1 sub main feeds a bio mass boiler and an outbuilding.

L2 sub main feeds solar and a pump room.

Phase one had a L to Earth fault damaged cable touched the tin foil wall insulation.

Caused 3 rcbos to trip in various locations, 2 of them on the opposite phase.

The fault being all Upstream of these rcds/rcbos.
 
To be completely fair, no one tells you at college to test for inter-connections.
This is one aspect where the ROI (AFIK, not worked there) has a good policy or requiring testing to show that all circuits are independent.
It normally takes a nightmare experience to begin to appreciate the value in some interconnection tests before a shared RCD or no-RCD board change!
Indeed!

Being a bit paranoid after discovering a friend's house had two crossed-connected RFC, as well as lighting borrowed neutrals, I try and IR between circuits before they go back in for use.
 
Hi,
I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted.
The issue i have is that when i connect one of the three lighting circuits it trips the other two lighting circuits together with one of the 32amp ring circuits!!!
I thought borrowed neutrals at first, but why would the 32amp ring circuit trip at the same time???
Thanks for all the input - looks like a day of testing tomorrow.
I have tested between all the offending line and neutrals and none show any intercionnect - just to make it more interesting
 

Reply to RCBO tripping issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
466
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
837
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top