Discuss fused spurs in the UK Electrical Forum area at ElectriciansForums.net

L

leonhammond

i am considering starting an av install in the front room. on the wall i am considering i have a socket, which i would like to run a quantity of fused spurs off. these would be for the component parts if the install. i do not want a selection of double sockets each with a plug in, as i feel this would look kinda rubbish.

how many spurs could i run off this socket safely, assuming it is not already used as a spur. or would i need to install a dedicated feed for these spurs, thinking of 7 or 8 spurs.

thanks
 
If it's a ring circuit then you would need as you say to confirm that socket is part of the ring. If it is then your best way to do this spur of your socket into a spur unit. Then on the load side of that spur you can run as many as you wish.

You know though that if you bury the cable less than 50mm you will need to provide the cable with additional protection as per the regulations.

Also if you run the cable to far you may affect your disconnecting times for your protection device.

Well if you think that double sockets look naff, not sure why you would think 7/8 spurs wouldn't
 
I feel that that many double sockets, each with a plug and cable on show would look really bad, as with the fused spurs i could wire in from the back and then only have the face plates on show. i just think it would look more tidy
 
I'd rather stuff an 8 way extension lead out of sight behind the gear.
 

Reply to fused spurs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
232
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
389
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
578
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
643
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock