Discuss fuses on fridge freezers? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

P

philn

Hi there. Im new to PAT testing. I am confused as all the fridges/freezers I have looked at range from 55 watts to 135 watts and from what Ive been taught any appliance under 700 watts requires either a 3 or 5 amp fuse. However, all the above that I have seen have a 13 amp fuse and the CE rating plate says 13 amp. So what am I to do? Do I go by the rating plate or follow what Ive been taught and change the fuse? Answers greatly appreciated thanks :)
 
basically, the fuse in the plug is to protect the flex to the appliance in the case of overload or short circuit. as the flex on fridge /freezers is generally 1.5mm, 13A is correct. bear in mind that the appliance is basically a motor, which starts and stops frequently thru the stat, and so you will get repeated surge currents which will cause fuse blowing if 3A or 5A.
 
Ok thanks for the reply teletrix. So the below 700 watt rule isnt hard and fast then? If the appliance says it needs 13 amp then you go by that?
 
yep. manufacturers stipulate the fuse rating. the 700 watt rule is more for appliances not having motors or other devices which have a high surge current.
 
Hi there. Im new to PAT testing. I am confused as all the fridges/freezers I have looked at range from 55 watts to 135 watts and from what Ive been taught any appliance under 700 watts requires either a 3 or 5 amp fuse. However, all the above that I have seen have a 13 amp fuse and the CE rating plate says 13 amp. So what am I to do? Do I go by the rating plate or follow what Ive been taught and change the fuse? Answers greatly appreciated thanks :)
hi my fridge is a sumsung and it keeps blowing a 250ma fuse on the top of the fridge
 
The above thread discusses the fuse rating in the mains plug supplying the fridge.

I expect that the 250mA fuse is protecting an internal fridge circuit.

you need to have an appliance engineer investigate it, maybe one that specialises in Samsung.
 
also worthwhile checking with samsung if there's a recall on your model. could be an intrinsic fault.
 

Reply to fuses on fridge freezers? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
483
18 months ago I bought American style fridge freezer (this model). I have a two year warranty. I have already had two call outs to replace a...
Replies
15
Views
529
Today I had to PAT a microwave oven. All seems well, except it is wired in thin-looking cable: cable: 5.5 mm dia N wire with insulation 1.8 Bare...
Replies
4
Views
859
I have Liebherr fridge freezer and need to extend the cable from the appliance to the wall plug. The directions do not allow an extension lead to...
Replies
2
Views
859
Hi, The lights on the control panel no longer come on and the power off and on button isn't working either. I have noticed the light bulb in the...
Replies
0
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock