Discuss Fusing down for lighting..... in the UK Electrical Forum area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
Hi,

Just been and looked at a job done recently by a colleague.
SWA dedicated 16A supply from a garage consumer unit to a external socket outlet and bulkhead light with external switch on an adjacent patio.
He hasnt provided any fusing down for the light and external switch.. (i.e. via an external switched fused spur, as I would have probably done)
He has posed the argument that because he has wired the switch and light in 2.5mm cable that the 16A circuit OCPD is sufficient, but I am concerned that the bulkhead light fitting and external switch have current ratings <16Amp.
He says its no different from a 13A socket outlet being protected by a 32Amp MCB on a ring final circuit, which I can't disagree with him on.

Can anyone provide some clarity on this for me please?
 
A 13A socket on 32A MCB is totally different - it has the <= 13A fuse for OCPD on the switch and plug contacts!

Given that most light switches are 10A max and many light fitting are designed for lower OCPD I would not be terribly happy. However, with it all in 2.5mm cable at least the 16A breaker is ample protection for the wiring both fault and overload.
 
A 13A socket on 32A MCB is totally different - it has the <= 13A fuse for OCPD on the switch and plug contacts!

Given that most light switches are 10A max and many light fitting are designed for lower OCPD I would not be terribly happy. However, with it all in 2.5mm cable at least the 16A breaker is ample protection for the wiring both fault and overload.

Agree.

But there isn't technically anything wrong with it - it is a "fixed" load - you would struggle to fit a lamp in the holder that exceeded 10A therefore from an overload perspective no problem, and providing the Zs is low enough fault protection is there.

The only issue is if the luminaire' instructions state 10A max ocpd or similar
 
Agree.

But there isn't technically anything wrong with it - it is a "fixed" load - you would struggle to fit a lamp in the holder that exceeded 10A therefore from an overload perspective no problem, and providing the Zs is low enough fault protection is there.

The only issue is if the luminaire' instructions state 10A max ocpd or similar

Thankyou very much Guys and Girls.
Have just looked into it, the switch is rated at 20A anyway and the light fitting is just a GLS lampholder in a polycarb bulkhead (no internal wiring or gear) so have referred to reg 559.5.1.204 for justification
So Ive let him off on this one but politely asked that, in the interests of good practice, he get into the habit of fusing down lighting in any future similar circumstance!
 

Reply to Fusing down for lighting..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
219
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock