tickover

Morning all
I have been asked to wire a integrated garage that is being converted into a Kitchen/dining room. there is an old wylex 4 fuse board in there at the moment supplying a 32amp ring and 6amp lighting circuit to an upstairs bedroom and a 32 amp ring and 6amp lights in the garage. there is also a SWA feed (think its 1.5mm) to a shed that has its own main switch off this board. this is all being supplied by a 10mm2 swa cable from one of the home consumer units (fed under floorboards no RCD protection at this point).

:D
so what I have been asked to do is remove old garage circuits, leave the ring and lights for upstairs (this is for one bedroom only), add feed for 7.7kW (max) oven, Ring for 7 double sockets, lights ( 8 down lighters, 2 ceiling roses), feed for under cabinet lights and a feed for outside lights to be installed at a later date.

:confused:
so the bit that is starting to confuse me is ( been think about it far to much, customer is old industrial sparky and is saying it should be fine) will the existing 10mm2 feed from cu be sufficient the run is no more than 15meters long or do we need to upgrade to 16mm2 swa. and I guess I will need to put in an RCBO in on the source for the feed in the house cu board.

Too much Xmas food and beer scrambled me brain :) lol!

Cheers guys
 
You should calculate the demand for the kitchen, which will then dictate cable
size to feed the sub board.

I doubt 10mm will be sufficient to be honest.
 

Reply to Garage conversion in the Australia area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
767
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
870
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock