Discuss Garden Lighting help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
20
Just after some general advice.

Been asked to look at a job where a builder/landscaper has already laid cable for some garden lighting.1.5mm 3 core SWA ran in 4 seperate radial circuits from a CU at the shed, each about 20M in length, looped in/out at each point. Customer wants spike lights in the trees (which isn't an issue) and walk-over spotlights around the pathway (this is where my issue is). Having posted on a different forum I have been advised to avoid 230v lights and use ELV. I haven't ever had to do buried lights before.

My idea is to use a swa branch resin joint to terminate the swa and cable out to each light. Then connect either straight to a 230v light or to a IP68 driver.

My main concern is water ingress so my questions are:
1) I think I will need to use a driver at each light due to voltdrop. What is the best way to bury/hide them? Which ones are best for this?
2) Why is 230v such a bad idea? Surely if a good waterproof buried connection is made it shouldn't be an issue.
3) If there wasn't already the cable there how would you usually do an install of this type? (i.e over this sort of distance etc)

Regards

Tom
 
Just after some general advice.

Been asked to look at a job where a builder/landscaper has already laid cable for some garden lighting.1.5mm 3 core SWA ran in 4 seperate radial circuits from a CU at the shed, each about 20M in length, looped in/out at each point. Customer wants spike lights in the trees (which isn't an issue) and walk-over spotlights around the pathway (this is where my issue is). Having posted on a different forum I have been advised to avoid 230v lights and use ELV. I haven't ever had to do buried lights before.

My idea is to use a swa branch resin joint to terminate the swa and cable out to each light. Then connect either straight to a 230v light or to a IP68 driver.

My main concern is water ingress so my questions are:
1) I think I will need to use a driver at each light due to voltdrop. What is the best way to bury/hide them? Which ones are best for this?
2) Why is 230v such a bad idea? Surely if a good waterproof buried connection is made it shouldn't be an issue.
3) If there wasn't already the cable there how would you usually do an install of this type? (i.e over this sort of distance etc)

Regards

Tom
If you're going to be using a driver at each lighting point, then imo you may as well use low voltage (mains).
You could use local transformers ?.
Certainly cost wise, low voltage is the way to go.
 
There's some useful? comments/ suggestions in the later part of this thread (eg post #35) from a while ago - if you haven't already seen it!
 
If you have just one constant current driver for all the lights at the origin, with the lights wired in series, then when one light fails open circuit, they will all stop working. Which as westward says, will be within 2 years.
 
Would that allow me to use just one transformer at the origin of the supply? What is the threshold for ELV?
Yes. Threshold is 50V AC or 110V ripple-free DC. @SJD makes a good point though, it's not a perfect solution. But none of the options are, it's a case of which one you feel is best.

230V will trip the circuit RCD if moisture gets into the lights/connections, and involves armoured cable which takes longer to install than flex. As @mainline says, multiple 12v transformers isn't great either.

This sort of thing can sometimes be done with a single 12V transformer though, depending on the circuit length and loads, voltage drop being the limiting factor.
 
So my main headache at the moment is that the cable has already been put in (not by me). It's 1.5mm 3 core swa and the runs are about 20-30 metres each. With approx 10 lights per run. I've never done buried lighting before so what would be the standard way to install walk over lights over this sort of distance and number of fittings if this job was being done from scratch (i.e cable not already laid).
 
Use Collingwood constant current ELV lights. Driver at source/consumer unit. Don’t worry about length of cable run. I did some recently to replace existing and it had total cable run of over 100m. Worked great. I’ve fitted hundreds of them now over 8 or 9 years. Only 2 failures (faulty batch said collingwood) quickly replaced with no quibbles. They’re not cheap, but I refuse to do it any other way. You get the odd driver failure, but the fittings are extremely good quality and won’t rust or tarnish and won’t let water in even if submerged
 
Oh that's interesting to know. How was the swa terminated at each point?
I have never fitted the lights you mention, but I have come across non working garden lights many times. It has mostly been to underground joints full of muck, water and ants. I have usually managed to persuade the customer to have a neatly placed post next to the light to house a weatherproof junction box. Of course, this is no help to you unfortunately!

When I was considering underground junction box for SWA the pratley box was mentioned on this site.
Here is a link Pratley 3 Way IP68 SWA Underground Armoured Cable Junction Box Size 0 - https://qvsdirect.com/products/pratley-3-way-swa-tee-box-under-ground-ip68-c-w-glands-shrouds-box-size-0

However well you do it, you may well find that in a few years you are called back because they are either not working, or tripping the RCD. It would be a good idea to make the customer aware that problems may arise down the line. I think I would also take some pictures of exactly where I had buried the boxes and save for future use as you may be digging them up again in the future.
 
What ever you do none of them will be working in a couple of years.
Ooh you synic! (Regrettably I agree, the only exception in my experience has been some stupidly expensive "designer" lights in a mansion I did, costing £238 per spike...)

@Roberts7286 , the prime reason for using extra-low voltage (ELV) outside is the inherent hazard of potential cable damage and the absolute requirement for RCD protection: anything electrical in the presence of water (damp/humid atmosphere, equipment like kettles and washing machines, outdoors, etc) will slowly experience it insulation breaking down and will produce nuisance tripping as over time an increasing amount of current starts to leak the wrong direction, capacitance increases, and other issues appear. Nearly always that part of the installation remains perfectly safe, but the rare occasion of actual fault in those environments involves elevated risk of shock or of causing undesirable influences on the rest of the installation and gives us the necessity to use RCDs. You can't avoid them, and they will produce nuisance tripping over time.

Also, because of the significant elevated risk of shock if you damage a cable in a wet enviroment, it must be installed with appropriate mechanical protection 100% of the way, requiring you to feed it through conduit and into junction boxes with IP-rated connections. Even SWA may be considered inadequate to directly bury at shallow depths, because a fork stabbed straight down over the centre of the cable will simply push the wire armour out of the way on its way down, like a bodkin arrowhead passing through chainmail into your loyal squire. If you damage ELV, on the other hand, it only causes your lights to inconveniently stop working. But as you will already be aware, the volts drop associated with ELV means installing thicker cabling than you first expect. Certainly at 20m length and multiple fittings I'd want to install at least 2.5mm or even 4mm (if a single fitting is at the end of 20m, your 1.5mm is probably adequate for 12V and certainly 50V). The only way to avoid that is more expensive Constant Current drivers and some proper maths to ensure it doesn't accidentally push more volts than is deemed safe.

Edit: my browser just refeshed and reveals a whole pile more messages in this thread! I only saw 3 to begin with. So this may be a repeat of other comments. I'll go do some reading now :)
 
Last edited:

Reply to Garden Lighting help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3...
Replies
4
Views
486
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
684
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock