Discuss Generator connection to mains supply questions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of power outages. The cable run from the generator to the outside mains incoming box will be about 40 meters. I intend to use 16mm SWA for that run. The generator control box has metering, fusing and an RCD. It's modern and made entirely by Mecc Alte. Not some Ebay Chinesium device.

Once the SWA is at the outside wall box where the underground feed from the supply company exits and the meter and master switch, 100 Amp utility company fuse is located, can I delete the two pole fused master isolation switch and use the two pole 125 Amp break before make change over switch and separate fuse as both an isolation switch to the house distribution panel and as a change over switch? I see a similar question was recently covered, but it was unclear as to whether doing this was advised against or regulated against.

Space inside the wall mounted outside box is limited. The alternative is to bring tails outside the box, to another water proof cabinet with the change over switch in, and return the cables back to the utility company box. Messy...

The property, a domestic bungalow, and has a PME earth system, how should the cabling from the generator be wired with regard to earthing at either end?

Thanks.
 
Can you post a picture of the meter box so we can be clear on what switchgear is currently installed in there?
I should be able to do that tomorrow, but basically incoming SWA service cable from underground to 100 Amp service fuse, then meter, then to a two pole fused switch and onwards to the consumer unit within the house. There are a couple of junction boxes in there, too, where outputs FROM the CU in the house splice into SWA cables to outside lights and to the garage. Thanks for your reply.
 
Here's a photo of the inside of the supplier's wall cabinet, the fused switch to the consumer unit inside the house has an 80 Amp fuse in it. The other fused switch has a 63 Amp fuse in it and serves a dedicated panel in the garage for a 63A socket for my TIG welder.
mains-box.jpg
 
Last edited by a moderator:
Looking at the wiring in that meter box I would suggest you employ an electrician as I doubt that the additions in that meter box have been ever been tested and parts do not appear to be compliant with the regulations

With a 2 pole changeover switch I would have concerns about the earthing still being connected to a PME system in the event of a power cut as it could be unreliable as an earth point and in the event of a fault could introduce fault currents into other properties located nearby
 
That looks rough, and there are boxes feeding various bits that kind of look like no over current protection, etc. As @UNG says you really should be getting that lot tested and documented before considering anything new.

As a first point of principle you should get an isolator switch that isolates everything, so all of the various things are down-stream of that including any transfer switch. It is the only safe and above-board means of working on the supply side of any CU to fit or fix the transfer switch, etc.

You must have an independent means of earthing any generator as you cannot assume the supply earth connection would be intact in the event of a fault that made you need to use the generator. A generator of that size would still be a TN supply (earth and neutral common at the generator) but that needs to be referenced to the true Earth by means of a rod or similar.
 
Althought the wall cabinet is owned and maintained by the property owner, the space inside is (supposed to be) reserved for the DNO and Energy supplier, apparently it's a condition of supply and is mentioned in their terms and conditions.

So if you are proposing altering any of what's there (excluding meter and fuse cutout) the simplest thing to do would be to move all the switch fuses to a new adjacent box and install the changeover switch in there.

If the meter needed to be changed to a "Smart Meter", either by request or the existing one going past it's use-by date or it failing, then I suspect the supplier would refuse to fit one as there would not be enough space.
 
OK, thanks for then replies, I imagine various things have been added on over the years and it has become somwhat of a pig's ear in there. What sort of secondary box would be required, are the regulations about that? I would like to have one mounted and ready for an electrician to populate, with any cable gland holes drilled to suit. Do cables between two boxes need to be SWA, or can T&E or tails in conduit be used? The SWA cable feed to the garage would really need to remain as it goes straight down into concrete and I will not be wanting to start digging up the concrete...
 

Reply to Generator connection to mains supply questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
888
How should grounding be made to a 20kVA single phase generator set feeding a domestic property via a manual change over switch? At the generator's...
Replies
17
Views
3K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
924
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock