Discuss Generator connection to mains supply questions in the UK Electrical Forum area at ElectriciansForums.net

Cables in the boxes must have secondary insulation, so tails (double sheathed single conductor) or T&E are fine as it is not exposed to UV light or likely to be damaged by rodents, etc. You should take care that any holes have protection to avoid damaging cable going between them so grommet, gland, conduit, etc.

The SWA coming up to that adaptable box could be tidied up with a new box and cable exiting to the new adjacent meter-style box (assuming it can go to the right of current one). I would re-do the cable gland so it has the cover for the exposed armour in place, though maybe it is tight to assemble it given the stupidly short bit left out of the concrete!
 
Cables in the boxes must have secondary insulation, so tails (double sheathed single conductor) or T&E are fine as it is not exposed to UV light or likely to be damaged by rodents, etc. You should take care that any holes have protection to avoid damaging cable going between them so grommet, gland, conduit, etc.

The SWA coming up to that adaptable box could be tidied up with a new box and cable exiting to the new adjacent meter-style box (assuming it can go to the right of current one). I would re-do the cable gland so it has the cover for the exposed armour in place, though maybe it is tight to assemble it given the stupidly short bit left out of the concrete!
Thanks, that's very useful, will order a new secondary cabinet and call the sparky.
 
Resurrecting this as I have been away. The electrician rewired the outside supply box and added a second box with the two pole transfer switch in it. He wired a 125 Amp socket in the workshop tp plug the generator into. What I find is the generator makes power and although the house lights work, the consumer panel RCD trips. I think only the sockets are on the RCD as all the house LIGHTING circuits work OK on the generator.

The generator has neutral and earth bonded n the alternator box and it has the chassis grounded to a six foot earth spike near the machine. The outside electricity board box states the supply is a multiple earth system. What would cause a presumed earth loop that would trip the consumer panel RCD please? The electrician is away abroad on holiday. .... Thanks.
 
He wired a 125 Amp socket in the workshop tp plug the generator into.

That should be a plug (aka inlet connector) and not a socket which is installed for the generator to connect to. The socket must be on the generator side of the connection.
What I find is the generator makes power and although the house lights work, the consumer panel RCD trips. I think only the sockets are on the RCD as all the house LIGHTING circuits work OK on the generator.

Does the changeover switch isolate the whole installation or does any part of the installation remain connected to the grid supply when the generator is in use?
 
That should be a plug (aka inlet connector) and not a socket which is installed for the generator to connect to. The socket must be on the generator side of the connection.


Does the changeover switch isolate the whole installation or does any part of the installation remain connected to the grid supply when the generator is in use?
The changeover switch is a 2 pole break before make affair, So live and neutral are switched. Gennie ground is permanently wired to mains ground in he service provider box. Thanks for your interest.

BUT, I have now found this out:

OK, nailed it I think to the consumer unit in the garage. House consumer unit has a 32 Amp MCB that I was TOLD was for the garage, and is marked as "Garage". With that and ALL other MCB's off on the house CU as soon as i turned the main house consumer unit isolation switch on the main RCD tripped. If I turn the master switch on the garage consumer unit OFF all is OK. If the garage CU is turned on, even with all the MCB's OFF, the house CU RCD trips and it's a 100mA one.

I just need to get my head around how the housebuilder wired this stuff up, and why, with all MCB's OFF on both the house and garage CU's but the main CU switches ON, and the garage CU master switch on, it trips....

On normal mains these all work as expected.

Anyway the gennie runs EVERYTHING in the house and workshop, including a rotary three phase converter and all the workshop stuff without even getting to half its load capacity, which was the main purpose of the installation test :)


One MCB in the garage consumer unit didn't like the inrush to an air bottle compressor and has had repeated resets over the years, maybe that MCB is knackered but I can't think why it would cause a Live / Neutral imbalance which is what should trip an RCD, surely?

Things may be clearer tomorrow whilst I get to grips of it in my mind. <LOL>
 
I can't think why it would cause a Live / Neutral imbalance which is what should trip an RCD, surely?
Have you verified the polarity is correct when running off the generator?

If the incoming L & N are correctly swapped between sources there is no adequate explanation for this problem. If they are actually reversing L & N polarity (even if down to the cable feeding the 125A plug) then you might have strange things happen, and it is VERY DANGEROUS.

A socket check tester in one socket that is working on both mains and generator ought to reveal if this is a problem or not.

And yes, the electrician who installed it should absolutely have checked this, but the problem you are reporting ought to have been caught as well.
 
It is also just possible that you have a N-E fault that is not apparent on the mains TN-C-S supply due to the very short neutral to the common point, but it becomes enough of a problem on the generator TN-S with a long neutral path back to the common N-E point.

Again, this ought to have been tested, a global IR measurement would show that up. Though if anything has been changed/disturbed after the changeover switch, etc, was added then it might not have been present.
 
It is also just possible that you have a N-E fault that is not apparent on the mains TN-C-S supply due to the very short neutral to the common point, but it becomes enough of a problem on the generator TN-S with a long neutral path back to the common N-E point.

Again, this ought to have been tested, a global IR measurement would show that up. Though if anything has been changed/disturbed after the changeover switch, etc, was added then it might not have been present.

Thanks again for the reply pc1966

My best pondering is done with a few pints in front of me and last night's session sat with dogs outside in the lovely evening sun gave me some good pondering time :)

What I believe is happening is there's a neutral to earth leakage in the garage after its consumer unit. The reason it is tripping a 100mA RCD in the house consumer unit only when the supply is from the generator and not from the mains is our mains voltage is rather low, under 220V a lot of the time.

The generator automatic voltage regulator is set at 245 to 250V (I need to check with a calibrated digital meter as the panel analogue gauge is probably none too accurate). I'm thinking Ohms Law is causing a higher current leakage at the higher generator voltage and it's then enough to trip the house consumer unit RCD.

What I really need is an AC low current clamp meter, but I don't have one and decent ones are expensive, so I'll have do it peasant's way and start disconnecting neutrals one by one in the garage consumer unit until it goes away. I'm suspecting an outside alarm PIR that played up then failed a couple of years ago. It may have water ingress. But we'll find out! What fun..... :(

I suppose I could lower the AVR voltage on the generator to say 200V and see if it stops tripping, but an excessive neutral to earth leakage needs fixing anyway. I'll try and do it properly.

I can see me spending hours in the sweltering and cramped loft space above the garage again, and I'm not as nimble as I was!

EDIT:

It's a fluorescent light circuit in a workshop fed off the garage consumer unit. I used a Megger to test every separated neutral off the busbar until I found one with 400 or so Ohms to ground. Of course it's the lights in my workshop with a car lift in it, so they are hard to get to "up in the Gods", but at least I now only have eight fluorescent fittings to check. Running all on gennie power as I type :)

Thanks for the help. Anything I may have missed or misunderstood please let me know but we've been on generator power, house and workshops, running all and anything for two hours with no issues.
 

Reply to Generator connection to mains supply questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
887
How should grounding be made to a 20kVA single phase generator set feeding a domestic property via a manual change over switch? At the generator's...
Replies
17
Views
3K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
922
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock