Discuss Generator formula in the UK Electrical Forum area at ElectriciansForums.net

Attachments

  • image.jpg
    16.4 KB · Views: 102
Don't forget that the relationship between rated kW and kVA for a generator is not necessarily the same as with a load such as a motor. The load defines the pf, so it is necessary to check that neither the maximum generator real power rating in kW nor the rated kVA are exceeded by whatever load is connected. Small generators are often rated for a nominal 0.8pf load and would be overloaded by a unity pf load equal to rated kVA.

If you want a more specific answer you'll have to ask a more specific question!
 
To add to what Lucien has posted......
Generators are, in my experience, usually rated at 0.8pf.
The ratio of kW/kVA.
The kVA will give you that current rating.
The prime mover, the engine, is often rated for the power, the kW rating.
That, in turn, limits the kW you can draw from the set.
So you can't get rated kVA at better than 0.8pf.
A 100kVA genny can't deliver more than 80kW.
 
To add to what Lucien has posted......
Generators are, in my experience, usually rated at 0.8pf.
The ratio of kW/kVA.
The kVA will give you that current rating.
The prime mover, the engine, is often rated for the power, the kW rating.
That, in turn, limits the kW you can draw from the set.
So you can't get rated kVA at better than 0.8pf.
A 100kVA genny can't deliver more than 80kW.
Thanks for that

is there any books that you know off that would be useful to read on this subject
 
Thanks for that

is there any books that you know off that would be useful to read on this subject
Books on that I don't have. Sorry.
Fowlers Electrical Engineer's Pocket Book was quite handy, I have a copy of the 68th edition, but I think it has been out of print for at least fifty years............:)
 
Re. power factor generally: any AC theory textbook. For generators specifically, application manuals and design guides from manufacturers might be helpful.
 

Reply to Generator formula in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
734
Hello everyone.. I'd like to know - what cable section should be with a three-phase asynchronous electric motor power of 132 kW, at a voltage of...
Replies
1
Views
803
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
555
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock