Discuss Generator three phase connections / cables in the Canada area at ElectriciansForums.net

H

Hades

Hi,

I have a 50kVA three phase generator. The installation is fascinating and I am interested in knowing what the electricians are taking into consideration when selecting the correct cable type. I dabble in low voltage electronics and circuitry and have a basic knowledge of the 17th Regs etc but am not a 'Qualified Electrician' and ask this question out of interest and the hope that I can lean something :).

The rated output is 70A and I spec that the min spec for any cable would be 25mm Singles (Copper), running in trunking together with the bonding. The cable run from the interlocks / control cabinet (for the generator) is ~3 meters. Given the environment it is possible that the cable may be exposed to oil and possibly diesel (in an accidental spillage).

I but would like some advice on the cable choice for these 3 meter runs? Are there any specific regulations that would cover these environmental conditions - i.e Generators and minor oil contamination?
 
I hope that trunking isn't attached to the generators terminal/connection box!! Normal PVC cables are pretty much immune to any occasional oil and diesel fuel contact, not so much if it's benzine. Cable raceways should always be run in such a manner as to avoid any such accidental exposure....

Control wiring, if not of the same voltage as the generator output, should be in a sheathed multi core cable, and it's insulation rated equal or higher than the highest voltage present in cable run encloses, or be totally segregated and run in it's own raceway...

There are many special cable types, go to a recognised cable manufacturer's web site and check out the many types available, and their uses...
 
I hope that trunking isn't attached to the generators terminal/connection box!

No it is not :). Also, the cable raceway is run to avoid accidental exposure. I hope that no one is using Benzine in the open air these days ...! :)). I am looking at Tri-rated cable.
 
You could do, It's what we use a lot on considerably higher rated Gen-Sets, it's flexibility is advantageous for vibration considerations. ...but as i say normal PVC cables should be more than adequate for your needs in this situation.

There are turbine Gen-Sets out there, that use aviation fuel, which is virtually paraffin!! lol!!!
 
yep, engineer, a lot of ppl don't know that jet engines run on paraffin. wouldn't like to try and run a piston engined plane on it though.LOL.
 
Don't know about the older prop engines, but the turbo props use aviation fuel too. It's not quite paraffin, it's a highly refined paraffin giving a higher octane level and lowering it's flash point for safety purposes with a few additives thrown in for good measure!!! Just don't ask me how, or about the chemistry involved!!! lol
That's the gist of what i was told by a company pilot anyway...lol!!!!
 
Diesel can react with PVC. Only last week I was storing some cable (T&E) in a lockup and a muppet builder split a load of diesel over the drums, rang up the cables manufacturers technical support and basically if its not removed fairly quickly it will chemically react (so I'm told) so I had to condemm the cable - couldn't risk it!
 
I think they were just covering there arses Yellowvanman, it would take a bit more time than that, to react with the PVC sheath, to the point of rendering it unusable... Iv'e seen some right bodge-up installations around fuel storage where cables have been saturated in diesel for god knows how long. In one case, the cleaners went in and cleaned the place up, couldn't really see any detrimental damage to the cables sheathing. These were SWA cables mind, not T&E, and there is i think a difference in the PVC make-up. Rarely see T&E overseas to be honest, it's more of a UK style house wiring cable than anything you would find on projects...
 
Last edited by a moderator:
I’ve never had a problem with diesel contamination on PVC cable. Some cable runs have literally been awash with the stuff.
The biggest problem comes with the vapour condensing in the control gear, add a bit of dust and wait for the fun to start.
 

Reply to Generator three phase connections / cables in the Canada area at ElectriciansForums.net

Similar Threads

(Thought I'd already poost this Q, but I cant see it, so I'll try again) We have some work going on in one of our buildings atm. On of the chaps...
Replies
7
Views
1K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
Replies
11
Views
1K
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock