Discuss Grounding a Wall Mounted Data Cabinet in the DIY Electrical Advice area at ElectriciansForums.net

J

Jin

I have recently taken over in the IT side of a medium company and one of the things I have noticed is a terribly installed wall mounted Data cabinet.

I have spent the weekend sorting it all out so it all comes up to spec but wanted to clarify on some points.

It is currently mounted on the wall but has not been earthed.
Power is ran from a 13amp BS 1363 from the trunking below to a small UPS in the cab. The UPS then breaks out onto a BS1363 PDU within the cab which is for a number of smaller DC powered devices (12, 24 and 48v transformers).

There is also a number of network switches installed (max, 250W), this is all grounded to an earth bonding bar that I have installed into the rack.

My question is, what do I earth the bonding bar to? Would it be acceptable to earth it to the earth in the ring main running below the wall mounted cabinet?
 
Does the flex feeding the cabinet not have a cpc
 
Does the flex feeding the cabinet not have a cpc

It does but some of the equipment that the UPS powers does not and this equipment is then has presentation elsewhere such as the router which is DC voltage but also connects to POTS or the CCTV.

Maybe I am being overcautious but I have always thought that metal data cabinets should always be earthed. Certainly seems to be the case for Data racks.
 
I can only comment from experience but whenever asked to install data cables and power for a cabinet it is requested by the data company that a 10mm bonding connection is made to the cabinet back to the consumer unit.
 
Whenever we installed wall mounted data cabinets we requested (from the electrical contractor) a dedicated spur to a twin 13 amp socket mounted above or to the side of the cabinet position with a 6mm bonding cable from the nearest board. (We'd indicate the required position by the use of a sticker when surveying the site taking into account the cabinet size, ceiling height, furniture and the route of the data cabling trunking etc.)
Then when the data cabinet was installed the 6mm cable would be bonded to the cabinet earth stud, not forgetting the cabinet manufacturer's bonding kit for the door and any detachable side panels.
 

Reply to Grounding a Wall Mounted Data Cabinet in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
390
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
465
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
212
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock