Discuss Happy earth rod day in the UK Electrical Forum area at ElectriciansForums.net

pc1966

Esteemed
Arms
Reaction score
11,984
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
 
Where was the other lead of the DMM, still the MET? Did you measure the AC voltage? That would cause a symmetrical influence on the resistance readings. I agree though that some electrolytic potential does usually show up that at least makes a difference between the two indications, or even swamps the DMM source making one of them negative.
 
Yes, it was basically the same test points. It was starting to rain so I didn't spend much more time checking AC volts, etc, but as the system is not finished yet there will be a more formal test when its all done.
 
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
10 ohms. That must get you an automatic nomination for "rod of the year award". Well done
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
Absolutely. I have never heard of such a good result. Very encouraging. Yes a great plan B for TN-S. But with those soil conditions another 2 rods could quite possibly get you a plan B for a TNC-S Istallation as well. Wish we had conditions like that over here
 

Reply to Happy earth rod day in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K
Hi, Can I ask some advice on what to bury please? This is the the front of my house in plan view. House at the bottom. Porch at the bottom left...
Replies
3
Views
2K
J
Hi I am having a few issues with the earthing at my house. This is a bit long winded but hopefully you can understand. I am not a time served...
Replies
37
Views
7K
B
Here's one that'll make you laugh then cringe,I was doing a replacement RCBO consumer unit for an old wylex rewirable fuse unit on a TT system...
Replies
39
Views
4K
Engineer54
E
T
Hi all, great site and sorry for the long post - I'm after some advice as I don't have total confidence in the 4 sparkies I've currently used with...
Replies
30
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock