I have an economy 7 boiler which has two temperature controlled heating elements. After 15 years they were replaced as they had started to heat inefficiently. Unsurprisingly they were covered in limescale.

I replaced them with new elements. The off peak element was placed on just over 50 degrees but kept on needing a reset so it was reduced to 45 degrees. After 6 months it blew up and the element needed replacing. It had split open and the fuse also blew.

I replaced both the elements with chrome elements. Same thing has happened again with the off peak element.

I am puzzled as to what is causing this and I am loathe to spend hundreds of pounds replacing them again.

I have one theory. My eco 7 off peak stays on all over the weekend. (Pls don't ask me why.) I think maybe that the element doesn't like staying on that much though I don't know how often elements check the temperature. I think that maybe the temperature control is malfunctioning meaning it heats up beyond what the temp is set at and then needs resetting as in the days before they blow it needs resetting a lot.

During the recent heat wave I hardly had it on and it was fine. As soon as it turned cold and had to some significant work it blew.

What can I do? Is it the electrics that are causing the problem and if so what action do I need to take.

The previous elements lasted for 15 years and worked great for 14.5 years without issue so I am puzzled why these new elements are breaking so quickly.

Thanks for any help or suggestions!

Rich
 
Do you not get 12 months warranty with the elements?
 
The plumber who installed them despite being a local, reputable firm has not been helpful in that regard. He said it would be hard to prove that the element was at fault.

Even if I got a refund of my £60 for the broken element it doesn't get me anywhere nearer to solving this problem.

It is strange that two consecutive elements have blown which would indicate it was not the element at fault. Or is it common that they blow like this?
 
My eco 7 off peak stays on all over the weekend.
It doesn't. There may be power to the element, but there is also a thermostat that controls the temperature. Once the water is heated (to whatever) the thermostat turns off the element, until the temperature drops.
When the element was changed, it would have been the best thing to chnage the thermostat as well.
 
Are you sure the thermostat is the correct length and type. I've come across the wrong length fitted, perhaps because that is what the plumber happened to have on the van, so it is not sensing the temperature in the correct place.
 
The most common cause of an element blowing open and splitting is dry running ie no water and excessive limescale build-up. You can pretty much rule out limescale if the plumber cleaned out the cylinder when the elements were replaced not long ago.

I'd also be wary of the quality of new items especially if the plumber is being unhelpful regarding a warranty claim, there's a lot of cheap rubbish on the market that's not fit for purpose. Usually a reputable wholesaler will happily entertain a warranty claim for a respectable brand name item if it was installed by a professional licensed plumber so I wouldn't accept him being 'unhelpful' if I were you.
 
I have an economy 7 boiler which has two temperature controlled heating elements. After 15 years they were replaced as they had started to heat inefficiently. Unsurprisingly they were covered in limescale.

I replaced them with new elements. The off peak element was placed on just over 50 degrees but kept on needing a reset so it was reduced to 45 degrees. After 6 months it blew up and the element needed replacing. It had split open and the fuse also blew.

I replaced both the elements with chrome elements. Same thing has happened again with the off peak element.

I am puzzled as to what is causing this and I am loathe to spend hundreds of pounds replacing them again.

I have one theory. My eco 7 off peak stays on all over the weekend. (Pls don't ask me why.) I think maybe that the element doesn't like staying on that much though I don't know how often elements check the temperature. I think that maybe the temperature control is malfunctioning meaning it heats up beyond what the temp is set at and then needs resetting as in the days before they blow it needs resetting a lot.

During the recent heat wave I hardly had it on and it was fine. As soon as it turned cold and had to some significant work it blew.

What can I do? Is it the electrics that are causing the problem and if so what action do I need to take.

The previous elements lasted for 15 years and worked great for 14.5 years without issue so I am puzzled why these new elements are breaking so quickly.

Thanks for any help or suggestions!

Rich

Does/did your system have a sacrificial anode(SA)? In certain water areas it can help enormously with corrosion.

The originals may have been high quality Incaloy or similar, very resistant to corrosion, coupled with a SA to give the long life.

I'm guessing the SA has corroded away, the new elements are cheapo (although you may have thought you were buying quality) and are only lasting a year.

Google galvanic corrosion and and sacrificial anodes.
 
Thanks for all your helpful replies.

I agree in retrospect it is suspicious that the plumber wouldn't provide me with the paperwork for the new elements. I asked numerous times before and after the fitting. I am writing formally to him.

The only thermostat in the system is that which is contained within the element. There is no separate thermostat.

I don't believe the system has a sacrificial anode(SA) nor were the original elements high quality Incaloy or similar. This is a shared ownership housing association block and everything was put together as cheaply as possible.

The first set of replacement elements looked identical to the originals. When the off peak replacement element split it wasn't covered in limescale unlike the originals. The chrome elements that replaced the first lot of replacements were slightly longer.

The system is a kernel direct plumbing unit produce code: 3396 installed in 2000. I can provide photos if helpful.

I've spoken to more of my neighbours and one of them said they had a similar problem with elements splitting. That neighbour didn't have a particularly solution beyond replacing the broken ones.

Can anyone suggest a good quality element to use this time?

Some of my neighbours have changed their set up completely, getting rid of economy 7, and moving to a pressure system. (Sorry not sure of the right term.) That's also an option.

Thanks again for your insights and suggestions.

Rich
 
The only thermostat in the system is that which is contained within the element. There is no separate thermostat.
I have never, ever seen that.

Inside the immersion housing for the element (under the top cover) there is a separate, removeable thermostat. The stat can be changed without draining the tank.

Please post a photo of the immersion connections.

Screenshot 2018-10-08 11.51.50.png
 
Sorry, that is what I meant by saying the thermostat was part of the element. Photo attached. If the elements are splitting though what good will changing the thermostat do?

IMG_20181008_115737.jpg
 
The blue bit is the thermostat and just pulls out.

If the stat is faulty, it may be powering the element too much. If you turn the red temp control you should hear it click as it switches on and off.
 
Thanks. I certainly think it possible that the stat has been faulty on the last two elements. Or at least unable to deal with the economy 7 being on all w/e. I started both elements at between 50 and 55 and as they reset gradually went down to 45. However by that time I think they had become faulty and the stat had completely failed leading to the splitting. That's my theory anyway.

Can you recommend a high quality element which the thermostat is less likely to fail?
 
I cannot find your system which you described as 'The system is a kernel direct plumbing unit produce code: 3396 installed in 2000.'
Some photos would be helpful.
 
Do you mean the reset button kept tripping. If so, the stat is definitely faulty, they operate at 90C to stop the tank boiling.

You have a standard thermostat. Pull it out and measure the length. You can buy a new one at most DIY sheds, Screwfix, plumbers merchants.
Make sure it has an over temp cut out included in it.
 
When was the last time the sacrificial aluminium protector rod was inspected and changed? See third image down.

What kind of water do you have - hard or soft?

Is the tank copper or stainless steel?

What length elements have been used for top and bottom positions?
 
Thanks for your feedback on the thermostat. I will bear that in mind in the future however at the moment a change of thermostat wouldn't suffice as I am pretty sure the element has split again.

In terms of the sacrificial aluminium protector rod - do you mean the piping impacting the corner of the sticker? Whichever one you mean I am pretty sure the answer is never though thinking about it a new one might been put in when I had a new pump installed last year.

I am in London so the water is very hard. I don't know if the tank is copper or steel.

I don't know the lengths of the elements. The first ones that survived for 15 years and their initial replacements were the same lengths and identical in all other superficial regards. The newer chrome ones were longer.

The top element is still functioning without issue and that was the case before, which makes me thing the thermostats of the bottom elements have been less than resilient and have been failing under approx 70 hours a week use.
 
I reckon you bottom element is sitting in/on or just above a thick later of limescale deposits . This means there will be insufficient convection currents of water around the element's surface area. Thus the immediate few centimeters of water around the element will be hotter and the surface temperature of the element will be higher. The overall result is that to achieve a heat flux of 3kW into the water the element will be operating at a higher temperature and for longer. Locally at the element the temperature is likely to be higher/or become higher than the boiling point of water (which is 100C at standard atmospheric pressure). The element is not designed to operate in this way for long.

I think (ie: what I would do) you need the tank draining of water, the bottom element removed and a torch shone through the boss to ascertain the limescale problem at the bottom of the tank. You can then scrape out/suck out with a wet vacuum cleaner the limescale and refit a hard water element of the correct length, or decide to replace the cyclinder in toto. Ask your plumber to cost for both repair and replacement before he starts.

And at the same time get the aluminium sacrificial rods replaced for new ones and record the date when this was done and when they next want replacing. I cannot see any flange in the images for something like these:

Protecting hot water tanks & heaters from corrosion - https://www.hamworthy-heating.com/Knowledge/Articles/Corrosion-protection-for-water-tanks-water-heaters
 
Last edited:

Reply to heating element problems with economy 7 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
557
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
379
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
856
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
420

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock