Wht would a star delta starter burn the motor out?
A star delta starter will in effect put 380/root3 volts across each winding, on start up, wouldn't it? into delta after a predetermined time the starter would change over and slap 380/400 across each winding.
The only way delta would burn out the motor would be because the mechanical load is to much, thus causing the winding's to overheat and burn out, purely a mechanical problem, that's why 3 phase squirrel cage motors are sometime started via a S/D starter, Star low voltage high torque Delta higher voltage lower torque due to the increased speed on star start up.
I agree Starting and running in Delta would probably burn the winding's out, but this will be due to overheating at a higher torque, nothing to do with the winding getting 230 v or 380 v, perhaps Westward's comment of more Motor knowledge is required is a bit wrong don't you think?
 
could comment but it'sbrd time and after beer so i wiattill timmirrow.
 
A star delta starter will in effect put 380/root3 volts across each winding, on start up, wouldn't it? into delta after a predetermined time the starter would change over and slap 380/400 across each winding.
The only way delta would burn out the motor would be because the mechanical load is to much, thus causing the winding's to overheat and burn out, purely a mechanical problem, that's why 3 phase squirrel cage motors are sometime started via a S/D starter, Star low voltage high torque Delta higher voltage lower torque due to the increased speed on star start up.
I agree Starting and running in Delta would probably burn the winding's out, but this will be due to overheating at a higher torque, nothing to do with the winding getting 230 v or 380 v, perhaps Westward's comment of more Motor knowledge is required is a bit wrong don't you think?
pete.you're missing the point.the motor is designed for 230V across each winding.on a 415 3 phase supply that's only in star. delta would put 415 on each winding. can only be delta on a 230V p-p supply.
 
pete.you're missing the point.the motor is designed for 230V across each winding.on a 415 3 phase supply that's only in star. delta would put 415 on each winding. can only be delta on a 230V p-p supply.
A special Motor then?
 
Last edited:

Reply to HELP 3 phase masonary saw wiring in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
646
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
669
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
905
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock