Makes no odds
I was trying to make merry Pete
Discuss Help - melted plug - why? in the DIY Electrical Advice area at ElectriciansForums.net
Makes no odds
Sorry Mate understoodI was trying to make merry Pete
A bit long winded but YesFrom an electrical point of view it would be best to have a specific 16A radial circuit for the heater on a higher rated (16A+) plug and socket arrangement.
The rating of the immersion means that it is pulling the maximum current that a BS1363 socket should take so any slight anomalies may cause melting such as you have seen. The same thing happens with standard immersion heaters on plug and socket or fused spur arrangements.
With the circuit installation you have you are unable to avoid requiring a 13A fuse at some point, presumably the wifi socket may be fused, the plug in the wifi socket will be fused and in the current set up the plug on the outside is also fused.
Each fuse (and each connection) is a potential point of failure.
The wifi socket must also be close to its rated limit as they are often limited to 10A or even 5 A.
The simplest solution would be to have a 16A socket installed outside instead of the double socket and still plugged in as you have it now inside, however this will only transfer the possibility of failure to the wifi socket and the plug which is used inside and will not address the heavy loading on the ring, although if it is only used at night the loading on the ring will probably be low.
GN1 advises a plug and socket set up for connecting immersion heaters is not recommended id imagine due to the 13amp plug and fuse being subject to their maximum loading for lengthy periods of time daily.I believe somewhere there is a requirement for immersions not to be on plug tops but I doubt this instance is applicable.
What does it show, when plugged into the socket without the Wi-Fi thing?
i.e. socket turned off?
@OP. if this appliance is in your van, does that mean that you plug it in at customers' premises. i.e. on site, as opposed to at home? if so, you would risk overloading their circuit/s. only solution would be to replace the heater with a lower power unit.
I imagine you would need a circuit from your CU to a 16 Amp socket, your heater would require a 16 Amp plug top to enable you to plug it into the 16Amp socket wired from your CU how you would manage at the customer premises is a different problem.That's a good point. Usually I plug it in at home and turn it on for an hour before I leave. It general stays hot enough all day - so I don't need to plug it in.
But on occasion I do plug it in at customer's houses via my extension lead and have never had a problem. Although as the tank is already warm, I doubt it 'fires' for long before reaching the required temp.
The other guy who I work with has been doing this job for 13 years, and has used this set-up for all that time with no issues - except for the element blowing every three months or so (although that's probably more to do with the sodium hydroxide in the tank!)
So - would the best solution (given that there's is some debate about best practice) to run a dedicated feed from the CU out of the house and to a 16A rated socket with 16A plug?
As I need to plug it into the van would a 16A socket and plug (on the element) in the van also be required? I'm presuming so.
easy. a short ext.lead 1363 plug on 1 end and a 16A commando socket on the other.I imagine you would need a circuit from your CU to a 16 Amp socket, your heater would require a 16 Amp plug top to enable you to plug it into the 16Amp socket wired from your CU how you would manage at the customer premises is a different problem.
It won't necessarily trip the entire CU just the circuit you have plugged into, which won't do much for customer relations, especially if they are on line etc.Yeah. Think that's always going to be an issue (customer's houses). I did consider fitting a split charge system (similar to the one on my camper) which powered a 12V heater for when I'm between jobs.
Although if everything's 13A and is only connected for a short time is it 'really' an issue? Isn't the worst that can happen it trips their CU?
The peak wattage could down a bit on the extension lead round the customers ....But on occasion I do plug it in at customer's houses via my extension lead ..........
- except for the element blowing every three months or so
OP I'm sure you comply with all the legislation regarding the transporting and use of chemicals in the course of your business.
I'm sure your training would have covered H&S, PPE and more importantly equipment. If you don't mind me saying, it doesn't appear you have your equipment quite right. The melting plug to one side, I'm not sure about the use of equipment fashioned by yourself, and the plugging in this equipment at your customers property.
I think you now have suitable advice from members on the way forward for your install to provide a supply for your equipment; do you think you should go elsewhere to seek guidance about how this equipment is installed & used in your vehicle?
@OP. if this appliance is in your van, does that mean that you plug it in at customers' premises. i.e. on site, as opposed to at home? if so, you would risk overloading their circuit/s. only solution would be to replace the heater with a lower power unit.