Discuss Help! New 2.5kW oven + 6.7kW hob - 40A fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi. I need to replace an old oven and hob. Currently the oven is 2.3kW and the hob is 5.8kW. They are both hardwired into the same connection unit, then it goes to a 45A cooker switch with an integrated 13A switched socket, then it goes to the 40A fuse in the consumer unit.

The new oven is 2.5kW and the new hob is 6.7kW. Fragments of spec below.

BEKO HIC64402T Ceramic Hob

Hob power - Front right: 1.5 kW / Front left: 2.2/0.75 kW / Rear right: 1.7 kW / Rear left: 1.2 kW

Electrical installation - This product requires hardwiring to a 32 Amp fuse.

Power supply - 32 Amp (Requires hardwiring to a dedicated cooker circuit)

BEKO Pro BXIM35300X Electric Oven

Energy consumption - 0.94 kWh

Electrical installation - This product requires hardwiring to a 16 Amp fuse.

Power supply - 16 Amp (Requires hardwiring to a dedicated circuit)

Electrical power rating - 2.5kW


The question is - are these new appliances suitable replacements or should I look for something with less total kW? Will the total load be too much while cooking on the hobs and using oven at the same time? We very often also use the integrated socket in the cooker switch while cooking to charge a mobile phone etc.

Thanks,

Piotr
 
The cable is 6mm. About 6-8 meters from consumer unit with 40A fuse to 45A coocker switch with integrated 13A switched socket and then to connection unit behind the oven. Both oven and hob connected to the unit. All other sockets including fridge are on a separate ring/fuse.
 

Reply to Help! New 2.5kW oven + 6.7kW hob - 40A fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
645
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
884
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
837
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock