Discuss Help with a transformer in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have a 110 5kva transformer. Run it off a 30 meter exstension lead running from the house into the Work shop. The transformer works and powers all machines
I've now installed a 6 mm armoured cable running length 30 meters on a 32amp breaker to the woek shop. When plug the transformer into the work shop sockets it trips the breaker. But socckets runs every thing else with out tripping. What could be the problem ?
 
Have you tested the ZS at the end of the SWA? Only thing I can think of personally is when it's initially powered up there's a slight surge but does sound a little odd.
 
Have you tested the ZS at the end of the SWA? Only thing I can think of personally is when it's initially powered up there's a slight surge but does sound a little odd.
Just tried a exstension lead in the work shop. Now that powers the transformer Fine. Just a direct plug to sockets to the sockets trips. Just cant think why
 
Just tried a extension lead in the work shop. Now that powers the transformer Fine. Just a direct plug to sockets to the sockets trips. Just cant think why
The added resistance of the extension lead (probably 1.5mm at most) is much more than the 6mm SWA, so any surge from the transformer now lacks that extra mitigation.

As @westward10 says you need to tell us more about the type of MCB, etc. Often for transformers a D-curve is used to avoid such trips, but that also has issues of achieving low enough Zs to meet disconnection times.

For a 5kVA transformer at 230V Hager recommend wither 63A C-curve or 32A D-curve. A 32A BS88 fuse has easier-to-meet Zs for similar surge capacity, but not nearly as convenient as a MCB.
 
For a 5kVA transformer at 230V Hager recommend wither 63A C-curve or 32A D-curve. A 32A BS88 fuse has easier-to-meet Zs for similar surge capacity, but not nearly as convenient as a MCB.
I would add that those MCB recommendations are for fault protection, not for overload protection of the transformer. It might have its own protection on the primary (230V) or on the secondary (110V) sides, but check the manufacturer's recommendation for supply protection first.
 

Reply to Help with a transformer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
889
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Replies
2
Views
1K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock