Discuss Help with specifying a long 4-core SWA run please in the UK Electrical Forum area at ElectriciansForums.net

Mark42

-
Esteemed
Patron
Reaction score
322
I need to augment the underground supply to remote workshops at my own house.

I’m struggling to understand the practical implications of voltage drop, rather than using blind compliance with recommendations/tables/regulations which do not take account of individual circumstances.

Here’s the spec:
  • A three phase x 100A TNC-S supply at the main house
  • A 220m run from the main house to the workshops. Will be local TT (wet clay).
  • Long-term loads at the workshops are mainly heating panels. If everything were on at once, it would be possible to use about 8kW of heating on any one phase. But never on all three phases at the same time.
  • The only three phase loads are trivial roller shutters, a 5kW compressor and a 2kW dust extractor. Both are lightly used, and never run continuously.
  • There are many other occasional SP loads, like a power saw, computers, blown-air diesel heater, and lights which are now all LED and relatively trivial.
The question is what size 4-core SWA do I need to use?

Cu prices have gone up massively and I need to consider cost. Or maybe aluminium sectoral cable? 4 x 35mm Cu is OK, 50mm is scary, and 70mm economically impossible. Runs of this size and length are beyond my experience.

The actual voltage on this rural site is 250V+. NOT the 230V we are supposed to use in the tables. Does this affect the practical implications of transient voltage drops?

ie Why the obsession with adiabaticity? If there’s a temporary underground cable ‘overload’, when say the compressor or a saw is used for 20 minutes, and a few degrees of heat is generated in the underground cable, then so what? It’s a waste of energy of course, but it will never cost me the thousands of pounds in additional copper indicated by the tables.

The buildings are currently supplied by a legacy 3 x 10mm, which shows no sign of heating at the terminations. But I am careful and watch the loads. I will in future rent these buildings for short-term research work, so this needs to be done properly, without me worrying about the upstream 32A breaker tripping. I’d much prefer to be able to fit a 40A B-curve, or even a 40C.
 

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V

Load:8kW / 14.43A

Length:220m



Cable Size:10mm²

volt drop 17.6
percentage 4.4
load 20amps
and no smoke paper insight .lol.
 
Last edited:

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V
Load:8kW / 14.43A
Length:220m
Cable Size:10mm²
volt drop 17.6
percentage 4.4
load 20amps

and no smoke paper insight .lol

Thanks but it's around 8kW of domestic heaters on each phase, not a single 8kW three phase heater! (2.7kW = 10.8A @250V - that would be easy ?)

Plus I need to allow for other loads, so the calcs are best done for say 10kW/phase.

One of the problems is that in winter, all the heating would go on together each morning for a few hours until the rooms warm up, when they would switch in and out intermittently, providing diversity.

I'd plan to blast the place with the very noisy 45kW diesel heater before the client/s turn up, then use the electrics for maintenance.

Everything's going on new 'Heatmiser Neo' thermostats, so complex (and remote) timed control will be easy via the app. That give me a lot of control over the total instantaneous load, but I have to allow for daft clients who bung everything on manually, all at once. And then plug their their machines into the 'wrong' sockets, overloading one phase.
 
Sticking in 220m and 30kW (i.e. 10kW/phase) an on-line calculator comes up with 25mm, so cost is around £2.5k or so plus VAT for 4C copper SWA.

Going to aluminium cable can save money BUT comes with a lot of extra trouble. It is very much more brittle and you need special care with termination materials/type/compounds to avoid corrosion and hot spots forming. Typically you need 1.5 times the CSA or 1-2 steps up in size (so maybe 35mm Al). However, aluminium is rarely seen under 70mm or so in SWA.

If you want to save a bit on the cable can you arrange for better balance of your heating loads across the 3 phases, etc?

Unfortunately it is not likely to be at the point where the cost of transformers makes up for the possible saving in cable (that also has all sorts of added complications).
 
ie Why the obsession with adiabaticity? If there’s a temporary underground cable ‘overload’, when say the compressor or a saw is used for 20 minutes, and a few degrees of heat is generated in the underground
The adiabatic limit is generally used for overloads/faults of around the 5s or less disconnection times typically planned for at the design stage. Its assumption is the temperature rise is due to the short-time fault energy heating the conductor quickly so little heat is lost to the surroundings.

For modest overloads, say in the minutes region, then your typical OCPD trip behaviour is matched to the cable already i.e. if the OCPD is <= cable CCC then all overloads and faults are protected against and it allows for heat escaping.

However, for any modestly long cable run you end up with the volt drop dictating the cable CSA (not heating effects), and usually if you meet the VD limits then your fault current is going to be high enough for safe quick disconnection. But almost never with TT, which is why the RCDs come out...
 
The adiabatic limit is generally used for overloads/faults of around the 5s or less disconnection times typically planned for at the design stage. Its assumption is the temperature rise is due to the short-time fault energy heating the conductor quickly so little heat is lost to the surroundings.

For modest overloads, say in the minutes region, then your typical OCPD trip behaviour is matched to the cable already i.e. if the OCPD is <= cable CCC then all overloads and faults are protected against and it allows for heat escaping.

However, for any modestly long cable run you end up with the volt drop dictating the cable CSA (not heating effects), and usually if you meet the VD limits then your fault current is going to be high enough for safe quick disconnection. But almost never with TT, which is why the RCDs come out...

Thanks. all good stuff, which I'd long forgotten!

And you're right about Aluminium. I'll forget that idea.

So does that mean that I can choose the OCPD primarily on the cable CSA/CCC alone? So a 40C breaker is (obviously) fine on say 35mm, even if it's over 200m long? Any gross fault downstream would trip a local MCB (none of which exceed 20A) before the supply main cable began to warm up significantly. A fault on the buried supply cable itself is unlikely.

There are three separate TP DBs in the workshops. One has a 30mA RCD incomer, the others have multiple RCBO circuits.

There's currently a historic mixture of 'exported' PME, and multiple local rods earthing the metallic building structures. I haven't yet checked the local earth impedance or PFC.
 
So does that mean that I can choose the OCPD primarily on the cable CSA/CCC alone? So a 40C breaker is (obviously) fine on say 35mm, even if it's over 200m long? Any gross fault downstream would trip a local MCB (none of which exceed 20A) before the supply main cable began to warm up significantly. A fault on the buried supply cable itself is unlikely.
Not quite.

You have two forms of protection and they are quite separate issues:
  • Fault protection must be provided (so any short, etc, disconnects in under 5s/0.4s for a TN sub-main/final circuit)
  • Overload protection is usually required, but not always for fixed loads (so the OCPD goes before thermal damage to the cable)
You can have one but not the other. So you can have fault-protection OCPD that clears a short but allows the cable to roast, or overload protection that stops a fire but fails to disconnect a fault in any sane time-scale (typically if you fail the VD requirement for the OCPD rating even if you meet it for the expected load on long cables).

In this case you have around 220m of cable, and if my earlier guess at the VD parameters are right, it is 4C 25mm and you plan a 40A OCPD so from the OSG tables.
  • 40A BS88-2 fuse has 1.0 Ohm (5s)
  • 40B has Zs max of 0.88 Ohm (0.4s & 5s identical)
  • 40C has Zs max of 0.44 Ohm (0.4s & 5s identical)
  • 40D has Zs max of 0.44 Ohm (5s)
From the Prysmian SWA data sheet 25mm 4C has R1 = 0.727 ohm/km and R2 = 2.3 ohm/km, so R1+R2 = 0.67 ohms at 220m. Running 16mm CPC in parallel with the armour is another option, so R1+R2 is around 0.33 ohm then if Zs is 0.11 ohm you can use any of the above, otherwise you are forced in to 40A B-curve, or a fused-switch.

Looking at the Hager catalogue, a 20A B is selective with a 40A B upstream MCB to around 0.4kA, and to around 0.5kA with a 40A BS88 fuse, so not much difference. But oddly a 20A RCBO is only selective with 40A B MCB to around 0.18kA.

If none of them are usable due to Ze being too high then you are looking at a supply-side delay RCD for fault-to-earth disconnection and then you might even go with a D-curve MCB for overload protection if final circuits all are RCBO so selective with the supply delay-RCD.
 

Reply to Help with specifying a long 4-core SWA run please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
492
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
519
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
841
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock