in fact my first time switching was last week standing very much alone in a switch room trying to work out how to get the RMU out of earth and praying that nothing further down the line was earthed out then closed my eyes and pulled the lever, pretty terrifying! I then had to repeat the exercise in a temporary substation standing 2 feet from a 2000KVA oil filled transformer in a steel box,
This isn't scaremongering and IS meant to scare the Cr*p out of you,,
Do not pray that everything down the line is not longer earthed, BE ABSOLUTELY CERTAIN IT ISN'T.
I never did HV switching but over my last 25 yrs of work was present many times during switching for 11kv transformer replacements or tap changes by suitably trained and experienced contractors or maintenance on the network switches by local DNO.
I was not present at this incident but did visit the customers site afterwards.
A contractor for the DNO had been testing part of the local HV ring, his colleague was at the other end with the test box across the lines.
Somewhere along the way they got out of sequence (poor comms) and the guy at the customers end restored power to the section they had been testing.
The test box was still inline.
Statement from the contractor a few days later when he had calmed down enough to talk,,
I made the switch, I heard the rumble, I ran out of the substation, I remember waking up sometime later.
I beleive he suffered concussion and shock and probably never worked again
The door had been blown off the substation, the roof had been lifted and had landed back on the substation.
The contractor didn't get far out of the substation before being blown part way across the service yard., luckilly no moving vehicles and no obstructions for him to be thrown against.